Psv X Flanged Valves

psv flange pressure class relief pressure

This topic has been archived. This means that you cannot reply to this topic.
3 replies to this topic
Share this topic:
| More

#1 marianine

marianine

    Brand New Member

  • Members
  • 7 posts

Posted 08 July 2016 - 07:23 PM

Hi everybody,

 

I have a doubt about change of the flange due to relief pressure. There is a PSV (sized to fire - overpressure 21%) located in a line of 600#. If you calculate the relief pressure, you will note that the flange of selected spec  does not support this value, but others components support. So I chose to stay with the same pressure classe for the line, however I specified the flange and PSV to 900#, adding the class break.

 

Nevertheless, I do not know regarding to the flange of block valve in the PSV inlet. Can I stay with 600# as it is an eventual situation (relief)? Or do I have change the pressure classe of line (full) to 900#?

 

Thanks,

 

Marianine

  



#2 Bobby Strain

Bobby Strain

    Gold Member

  • Members
  • 3,529 posts

Posted 08 July 2016 - 08:21 PM

You select the system components, including the PSV, based on design pressure, not relieving pressure.

 

Bobby



#3 marianine

marianine

    Brand New Member

  • Members
  • 7 posts

Posted 09 July 2016 - 05:34 AM

Thanks Bobby!

 

I have to select the components based on design pressure, because the relief scenario is an eventual occasion, correct?

 

Do you know any standard about this? Because I have to justify for a client the reason why I do not change the pressure class of the line.

 

Once more, thank you!



#4 latexman

latexman

    Gold Member

  • Admin
  • 1,686 posts

Posted 09 July 2016 - 07:44 AM

It should be in the applicable piping Code.  Overpressure allowances are built into the Code.  If you design to the design pressure and are in compliance with the Code, you are fine.