Sizing Control Valves Below Choking Pressure Drop


This topic has been archived. This means that you cannot reply to this topic.
2 replies to this topic
Share this topic:
| More

#1 Poosticks

Poosticks

    Junior Member

  • ChE Plus Subscriber
  • 14 posts

Posted 02 November 2016 - 07:02 PM

I am looking to size a control valve to be capable of reducing pressure in a liquid line (water) from 20 bar down to 2 bar. Running the sizing calculations in IEC 60534 I find that the flow would choke before I could reach this pressure drop. Does this mean that it is impossible to achieve the requirement in a single valve? Or can a multi-stage valve handle this?

I do have a little difficulty with multi-stage valves in that the current standards state they are for compressible flows only (their use as anti-cavitation devices does not really address my issue).



#2 Bobby Strain

Bobby Strain

    Gold Member

  • Members
  • 3,529 posts

Posted 02 November 2016 - 07:57 PM

Send your specifications to a reputable control valve supplier.

 

Bobby



#3 shvet

shvet

    Gold Member

  • Members
  • 135 posts

Posted 03 November 2016 - 10:36 PM

I am looking to size a control valve to be capable of reducing pressure in a liquid line (water) from 20 bar down to 2 bar. Running the sizing calculations in IEC 60534 I find that the flow would choke before I could reach this pressure drop. Does this mean that it is impossible to achieve the requirement in a single valve? Or can a multi-stage valve handle this?

I do have a little difficulty with multi-stage valves in that the current standards state they are for compressible flows only (their use as anti-cavitation devices does not really address my issue).

 

Your issue is typical for BFW pumps min flow lines (spillback). There is a lot of manufacturers that can suggest you a multistage CV (usually angle type). I agree with Bobby - send your specification to a reputable vendor.