What is the purpose of water seal at the bottom of dry gas flare? I have never seen this anywhere before.

It's more hazardous than it appears useful - especially when you think of e.g. flare overpressuring and blowing the flare gas out together with the water seal. Also, you have to check it from time to time and see if water is dripping out from the ground connection or not - and to refill the system as required? It looks quite stupid and hazardous in my opinion, but perhaps I'm wrong.

Attached File  Dry_Flare.JPG   70.38KB   125 downloads


#2 riven

riven

    Gold Member

  • ChE Plus Subscriber
  • 178 posts

Posted 25 May 2009 - 07:26 AM

I too am intrigued.

The only question I could ask is what is the water seal sealing against? And if its purpose is to seal against something, why not use a mechanical/different seal?


#3 djack77494

djack77494

    Gold Member

  • ChE Plus Subscriber
  • 1,282 posts

Posted 26 May 2009 - 08:19 AM

The water seal looks to be a configuration that permits any liquid that may condense within the flare stack to freely drain while still containing the potentially flammable gases within the stack. (I've never designed a flare system, so this is my "guess" based on other seals I have seen.) The seal prevents gases from escaping out the base of the stack because the gas pressure would need to build enough to overcome the height of liquid contained in the seal leg in order to escape.

#4 Guest_emathis_*

Guest_emathis_*
  • guestGuests

Posted 26 May 2009 - 09:54 AM


Typically, a water seal is a required safety device on flares to prevent flashback into the process especially when the user is a relatively low pressure user such as a tank vent. Flash arresters are used when the vent has sufficient pressure to handle the reqired Dp.

Your P&ID suggests that the seal is part of a vendor supplied package. If you research the vendor design you will find that the inlet gas enters via a diffuser below water level providing a few inches of water column back pressure on the user. Should the flare flash back, the flame front should be quenched sufficiently to prevent ignition of the vent piping and your process. Water seal level is typically an alarmed process measurement usually a permitted variable to allow flare ignition. Under normal operation little water overflows and, in fact, water addition is required to cover evaporation.

Not knowing the composition of your vent, water soluble components or condensable organics must be considered in dealing with the disposal of the seal water and general operation.

Hope this is helpful.

#5 JoeWong

JoeWong

    Gold Member

  • ChE Plus Subscriber
  • 1,223 posts

Posted 26 May 2009 - 03:52 PM

Besides what Doug proposed...

rain water is one of the concern especially in tropical country...

#6 chemtan

chemtan

    Gold Member

  • Members
  • 60 posts

Posted 01 June 2009 - 07:59 PM

I have designed Flare systems and evaluated the one under operation...

Emathis has already answered this in detail... Would just add that use of water seal is advised by API, see APIs 520 and 521 to find where\why water seal could be used.

Insurance guys would not want to work with you unless they believe your Flaring and De-pressuring system is correctly designed using recommended practices. And for this, they rely on international practices like APIs (atleast here in Pakistan) smile.gif

#7 Zauberberg

Zauberberg

    Gold Member

  • ChE Plus Subscriber
  • 2,727 posts

Posted 01 June 2009 - 11:59 PM


If there is no contact with air, there is no ingress of air - that was my question from the beginning.
This is a dry flare, and I believe an ordinary drain valve at the bottom of the flare (including the level transmitter) would serve the purpose in a more efficient and safe way.

#8 djack77494

djack77494

    Gold Member

  • ChE Plus Subscriber
  • 1,282 posts

Posted 02 June 2009 - 08:56 AM

I do not disagree with what you are saying here, and I am not recommending a water seal leg. Nonetheless, I liked JoeWong's comment of what about rain? I assume that the operations group would prefer to not have to check for liquid in the base of the flare and would definitely prefer to avoid the manual operation of draining off any liquid accumulation. So, I see no problem with the water seal. I do not share your concern with blowing the water from the seal, since this should not occur in a well designed seal leg. Your concern about the need to check and fill the seal leg is definitely valid and should be balanced against the effort required for the alternative. Ultimately, I think it's a matter of personal preference.

#9 astro

astro

    Gold Member

  • Members
  • 89 posts

Posted 03 June 2009 - 07:14 PM

QUOTE (Zauberberg @ May 25 2009, 05:15 PM) <{POST_SNAPBACK}>
What is the purpose of water seal at the bottom of dry gas flare? I have never seen this anywhere before.

It's more hazardous than it appears useful - especially when you think of e.g. flare overpressuring and blowing the flare gas out together with the water seal. Also, you have to check it from time to time and see if water is dripping out from the ground connection or not - and to refill the system as required? It looks quite stupid and hazardous in my opinion, but perhaps I'm wrong.

Attached File  Dry_Flare.JPG   70.38KB   125 downloads


I'm used to seeing this kind of flare / vent configuration and don't find it a disagreeable design on the surface. That said I would make improvements (see bottom of the post) depending on the risks and finding out further information.

I went searching in my 5th edition copy of API STD 521 and found section 7.3.4.2, 6th paragraph:
QUOTE
In every vent stack installation, careful consideration should be given to two potential problems:
a) accumulation of liquid in lines that terminate at the vent stack


The section goes on further to say:
QUOTE
Accumulation of liquid in lines to the vent stack can result from leakage into the system of high-relative-molecularmass vapours that condense at ambient temperature. If appreciable quantities of liquid collect, they will subsequently be discharged to the atmosphere when vapours are released into the system.

To avoid liquid accumulation, pockets should be prevented from occurring in the lines and the system should be sloped to a low-point drain. These drains can be installed to function automatically by using a properly designed seal. The height of the seal should provide a head equivalent to at least 1,75 times the back pressure under the maximum relief load to avoid release of vapour through the seal. As an alternative to a sealed drain, a small disengaging drum may be installed at the base of the vent stack. This type of installation is recommended where significant quantities of liquid can occur.


My comment to improve the design of the P&ID presented would be to include a local level gauge and consider instrumentation to address high level events due to rain or other causes (which need to be determined from evaluation of the normal & non-steady state operation and emergency scenarios via HAZOP or some equivalent technique). The action of the instrumentation being commensurate to the assessed process and safety risks.

There are downsides to any design selection. By adding some mechanism to prevent one problem, the result is that often another problem has been engineered into the design. Seal legs make a lot of sense because they offer a low ops/maintenance design but because of this they can suffer neglect and degrade to a latent failure mode (e.g. blocked seal leg). Other more "active" designs provide a counter position. Ultimately it's a balance of risk and your ops/maintenance philosophy, which the Engineer at the work face is in the best position to assess and understand.