Hello, I have a question with respect to the isolation valve installation standard for LNG Vaporizer.

 

As per NFPA 59A 2013 edition, where the heated vaporizer is located less than 50 ft from the heat source, it shall have an automatic shutoff valve in the LNG liquid line located at least 10 ft from the vaporizer.

 

Would you tell me why an automatic shutoff valve shall be located at least 10 ft from the vaporizer?

 

Thank you.



#2 Bobby Strain

Bobby Strain

    Gold Member

  • Members
  • 3,529 posts

Posted 10 April 2018 - 09:55 PM

Because the NFPA committee thinks it's a good idea. They probably took a vote to establish the distance.

 

Bobby



#3 Jay Kim

Jay Kim

    Brand New Member

  • Members
  • 3 posts

Posted 11 April 2018 - 08:06 PM

Thanks for your reply, Bobby.

 

If the isolation valve location shall be considered in accordance with NFPA, can I install it 50 ft from the vaporizer?

What's the reason automatic isolation valve should not be located within 10 ft from the vaporizer?

 

Thank you.



#4 Pilesar

Pilesar

    Gold Member

  • Members
  • 1,384 posts

Posted 12 April 2018 - 07:56 AM   Best Answer

In case of a fire, you want to have an isolation valve to shut off the fuel source.  The valve controls should not be burned up in the fire which would make it useless.  So put the valve outside the most likely fire danger area.



#5 Jay Kim

Jay Kim

    Brand New Member

  • Members
  • 3 posts

Posted 12 April 2018 - 08:28 PM

Thank you, Pilesar. Now I understand.



#6 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,954 posts

Posted 14 April 2018 - 01:45 AM


 

 

Jay Kim,

 

It's obvious the automatic SDV should be located outside the fire zone to be closed remotely to prevent feeding fire by LNG in fire case; of course if it has to be located inside fire zone it shall be fireproofed one not to be damaged when is engulfed in a pool fire...