Reboiler With A Hot Oil Jacket
#1
Posted 05 April 2020 - 05:09 AM
#2
Posted 07 April 2020 - 12:55 PM
Unless the jacket contains a big enough gas volume the pressure in the jacket would become gigantic when the oil is heated and therefor the jacket will require a PSV to protect it, and relieve the expansion when necessary. You can avoid the PSV to open during normal operation by installing a sufficient big expansion bellow in the oil piping.
But I really don't understand why anybody would design such a complicated system to provide heat to the bottom of a column.
Change the design: delete the jacket and pump, and insert a suitable heating element directly in the column bottom liquid.
#3
Posted 07 April 2020 - 11:55 PM
Hi,
To add to the other comments , a specification/operation sheet for thermal fluid (paratherm) where you can read the expansion volume ( about 10% for 100 c) .
Additional volume must be considered to take account the expansion together with a PSV where the discharge should be routed to a safe location (catch pot) .
Regarding the circulation pump it should be a centrifugal pump , more robust /reliable than an air diaphragm pump .
my view
Breizh
Edited by breizh, 08 April 2020 - 12:13 AM.
#4
Posted 08 April 2020 - 08:49 AM
Gentlemen,
Thanks for your recommendations.
An option to use a heating element installed directly in the reboiler was checked in the past.The biggest problem is to find a electrical heating element which is certified for the hazardous area (Class 1 Div.1), the heating fluid is n-pentane.
Thank you, Mike
Similar Topics
Kettle Reboiler Flow FractionsStarted by Guest_Lyne_* , 31 Mar 2024 |
|
|
||
How To Select Reboiler And Condenser Operating Pressures For A Mdea ReStarted by Guest_Alexis Azamar_* , 27 Mar 2024 |
|
|
||
Outlet Temperautre Of ReboilerStarted by Guest_hysyshunter_* , 18 Mar 2024 |
|
|
||
Types Of Reboiler And CondenserStarted by Guest_refluxraider_* , 17 Mar 2024 |
|
|
||
Kettle Reboiler LengthStarted by Guest_Lyne_* , 26 Feb 2024 |
|
|