There is an ongoing discussion at my refinery, regarding best practice for venting/blanketing of underground tanks, and I would very much appreciate your opinion.
We have a number of closed drain system containing hydrocarbons, which are drained into underground storage tanks. The drained hydrocarbons are not expected to be very light, but it depends on which system the drain is coming from. At present we have the following scenarios:
1. Underground tank with a free air vent (equipped with flame arrestor, and to a safe location)
2. Underground tank with a closed vent, connected to the main flare header
The older systems are installed following the first arrangement, but they require some type of area classification around the vent, and it is expected that the tank vapour area has an explosive atmosphere.
The newer systems are installed following the second arrangement, but experience serious problems during flare relief situations, due to backpressure from the flare system, and lack of liquid seal or other methods to prevent backflow of flare gas into the main flare header.
It is my opinion that underground tanks should remain with an atmospheric vent, or be connected to a gas blanketing system other than the flare system in cases where this is unavoidable. Unfortunately, I have not found any standard covering this situation.
I would be very interested in hearing the experience of others from the forum on this issue.