Emergency Vent Set Pressure For A Ulc-601 Tank


This topic has been archived. This means that you cannot reply to this topic.
2 replies to this topic
Share this topic:
| More

#1 Inniswhe

Inniswhe

    Brand New Member

  • Members
  • 1 posts

Posted 06 May 2011 - 10:47 AM

I was wondering if anyone knows the maximum emergency vent pressure setting for an atmospheric flammable liquids storage tank meeting ULC-S601 construction standard ?

Thanks

Edited by Inniswhe, 06 May 2011 - 10:48 AM.


#2 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,930 posts

Posted 06 May 2011 - 01:23 PM

I was wondering if anyone knows the maximum emergency vent pressure setting for an atmospheric flammable liquids storage tank meeting ULC-S601 construction standard ?

Thanks


It depends on the MAWP/design pressure of the tank.

#3 proinwv

proinwv

    Gold Member

  • ChE Plus Subscriber
  • 391 posts

Posted 08 May 2011 - 04:46 PM

Yes, you must know the MAWP as well as the MAWV to size vents. But you say an atmospheric tank, and look at the word, ATMOSPHERIC. Typically these have very little or no pressure capability.

Look for a nameplate or contact the manufacturer to determine its' capability.

Then, if you have any pressure capability, determine the required venting volume and size a vent that will not exceed your MAWP at that volumetric flow.