Can anybody provide guidelines for sizing of relief devices for glass (borosilicate) vessels?
They are used extensively in the pharmaceutical industry but there doesn't seem to be any information out there for sizing for a Fire case. Will such a vessel not rupture in a fire case long before the relief device activates?
Any information or suggestions would be gratefully received.
Thanks.
|
Pressure Relief For Glass Vessels
Started by Guest_Linus_*, Aug 26 2003 02:42 AM
1 reply to this topic
Share this topic:
#1 Guest_Linus_*
Posted 26 August 2003 - 02:42 AM
#2
Posted 26 August 2003 - 06:01 PM
If the vessel is not atmospheric, it needs some sort of overpressure protection. The calculation will be dependent on the code the vessel falls under. For example, if it is a pressure vessel (designed for 15 psig or more), then it will follow ASME Section VIII, Division 1. If it is designed for around 2.5 psig, it will follow API 620. Atmoshperic vessels follow API 2000.
The calculation for fire is irrespective of the material it is made out of. It just needs to follow the applicable code.
As far as the vessel failing before the relief device activates, this can actaully be said of any vessel, even steel. The relief device is used to control the release of vapors generated during the fire. Once all the liquid in the vessel evaporates, the vessel will probably fail, steel or otherwise. I've argued many times that the gaskets between the relief device (relief valve in my case) and the flange it is connected to will probably fail before all the contents boil anyways. Some have agreed and others not. But no matter, the code tells us to supply a pressure relieving device and we must do so.
The calculation for fire is irrespective of the material it is made out of. It just needs to follow the applicable code.
As far as the vessel failing before the relief device activates, this can actaully be said of any vessel, even steel. The relief device is used to control the release of vapors generated during the fire. Once all the liquid in the vessel evaporates, the vessel will probably fail, steel or otherwise. I've argued many times that the gaskets between the relief device (relief valve in my case) and the flange it is connected to will probably fail before all the contents boil anyways. Some have agreed and others not. But no matter, the code tells us to supply a pressure relieving device and we must do so.
Similar Topics
Valves On Low Pressure Steam ServiceStarted by Guest_Ali4269278331_* , 15 Apr 2024 |
|
|
||
Answered
Steam Pressure Requirements For Limpet Batch ReactorStarted by Guest_golegolegole_* , 10 Apr 2024 |
|
|
||
Pressure Control Valve Issues For Gsw LinesStarted by Guest_fahadazh_* , 29 Mar 2024 |
|
|
||
Vapor PressureStarted by Guest_Hamza1111_* , 23 Mar 2024 |
|
|
||
Answered
Vacuum Ejector Pressure ControlStarted by Guest_himanshu.ch_* , 19 Mar 2024 |
|
|