In order to reduce the risk level in one of our satellite platform, we intend to adopt a total blowdown philosophy instead to the partial one.
i.e: Process area is divided in tow fire zone: GL and Production. In case of occurrence of fire in one zone only this later is depressurized and the second one remain under gas.
We run the depressurization module in aspen hysys for three credible scenarios: fire case, adiabatic & minimum temperature.
Results show:
With the actual configuration and without restriction orifices on blowdown lines:
- Depressurization time in each separator is less than 3 min!!
- Total blowdown cannot be adopted: peak flow of one separator exceed the HP flare tip capacity!!
- Fire case gives us the highest peak flow.
With restriction orifice designed to get depressurization according API RP 521 criteria:
- Fire case gives the highest peak flow.
- Blowdown load (sum of peak flow from each vessel) is less than the HP flare capacity.
My questions are:
- There is other credible scenarios that shall be studied in our case? (note: only separators are installed in the platform and the HP flare tip was designed for the relief case “blocked outlet scenario in the main production separator”)
- Can we assume the blowdown load as the sum of peak flows?
- Shall we run simulation on ASPEN FLARE ANALYZER to confirm backpressure is not exceeding MABP during blowdown?