Limit On Psv Back Pressure

psv back pressure

This topic has been archived. This means that you cannot reply to this topic.
1 reply to this topic
Share this topic:
| More

#1 ayan_dg

ayan_dg

    Gold Member

  • ChE Plus Subscriber
  • 148 posts

Posted 21 July 2015 - 11:54 AM

If a gas flows through a orifice where the downstream pressure is less than critical pressure , the flow through the orifice is critical flow and depends on the inlet pressure , it is independent on the outlet pressure.
Now for conventional spring loaded relief valve we limit outlet back pressure to 10% of set pressure ( say for blocked discharge case ) , why this limitation is required because at say 15% back pressure or even at 25% back pressure the flow should be critical for most gases and hence independent of outlet pressure.

#2 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,951 posts

Posted 21 July 2015 - 12:25 PM

Now for conventional spring loaded relief valve we limit outlet back pressure to 10% of set pressure ( say for blocked discharge case ) , why this limitation is required because at say 15% back pressure or even at 25% back pressure the flow should be critical for most gases and hence independent of outlet pressure.

 

ayan,

 

Because the maximum accumulation in pressure vessel is 10% and it would offsset the maximum back pressure of 10% in order to the valve being full open. Then if the back pressure in conventional PSV to be higher than 10%, the PSV can't be in full open postion, hence rated capacity, otherwise the accumulation would reach the exceeded back pressure that in turn the code limitation would have been passed...
 