Low Sulfur Vacuum Residue As Fuel Oil In Furnace
Posted 24 December 2016 - 03:03 AM
Posted 24 December 2016 - 08:44 AM
LSVR? Please attach the P&ID so we don't have to draw it out.
Posted 24 December 2016 - 11:02 AM
Currently p&id is not available.
I have doubts regarding the steam line and condensate line control system. As only steam trap would be controlling the steam inlet flow.
Posted 29 December 2016 - 03:53 AM
the globe valve on steam inlet with TI on oil outlet could provide a rough manual control in steady conditions...
Posted 03 January 2017 - 09:33 PM
I agree. The burners should operate well over a viscosity range. I once had a plant manager look over a proposed design and say: "Too much instrumentation. If I flew over this plant and dropped a wrench, it would hit an instrument!"
Posted 07 January 2017 - 11:32 PM
Steam line size us 3inch. If steam trap works fine , can there still be a chance of any steam blow off through oil heater?
Posted 20 January 2017 - 09:08 PM
Hi Mayank,
I agree with others keeping the control simple should be fine. I suspect the limiting heat transfer resistance is on the viscous oil side.
The steam side will not be limiting as long as the manual globe valve is set open enough for times when burners(s) are needing maximum fuel flow, and as long as the steam trap capacity (and condensate return system) can keep up with the condensate generation. The steam flow will therefore vary by itself just to match the heat taken by the oil.
The exchanger should also occasionally be cleaned on both sides of the heat transfer surface.
Dazzler
Vacuum Pump Power EquationStarted by Guest_hysyshunter_* , Yesterday, 05:46 PM |
Answered
Vacuum Ejector Pressure ControlStarted by Guest_himanshu.ch_* , 19 Mar 2024 |
Vacuum DistillationStarted by Guest_hysyshunter_* , 12 Mar 2024 |
Issue With VacuumStarted by Guest_Aksu007_* , 29 Feb 2024 |
Reducing Steam Consumption In Vacuum Packed DistillationStarted by Guest_dpunnn_* , 30 Nov 2023 |