Hi,
At first, I would like to apologize for my long post.
I would like to seek some suggestions about a system that I am having trouble to handle with my calculations. In this regard I have attached the drawing of the system.
For the sizing of PSV-100, I have found the required relieving load to be 19000 Kg/hr (Fire Case).
The purpose of EX-100 (Emergency condenser), is to condense the unexpected vapor generated by overheating of the vessel during our operation. It is important to mention that the vessel is subjected to heating and cooling by internal and external coils for maintaining desired temperature.
In the case of finding required relieving load for PSV-200, I have considered V-2, V-6 and V-7 will remain closed while V-1 will remain open. If these things are assumed, then required relieving load calculation leads to the consideration of feature like that I have done for PSV-100 and results in 19000 Kg/hr (Fire Case).
Vessel protection.pdf 94.64KB 56 downloads
The main problem is that EX-100 has been designed for 46600 Kg/hr (vapor). It indicates that vapor will be generated in the vessel at the maximum rate of 46600 Kg/hr. Which is 2.5 times larger than the vapor generated during fire case (19000 Kg/hr). This flow rate could also be the flow rate that is faced by PSV-100 and 200. Even if I take whole vessel’s wetted surface, it doesn’t yield that amount of relief.
In that case, would I stick to my relief load calculation for fire case or I should consider 46600 Kg/hr for required relief load for both PSVs? Of course later will result in so much bigger PSV.
Any suggestion is highly appreciated.
Many Thanks.
Shahidul