Dear Respected Members
I am working on project for crude oil storage tank farm facility. in the terminal there are total 10 no of tank used to store crude oil product.
product specification is as follows.
Viscosity = 50 cSt
Density = 860-891 Kg/ m3.
Vapor Pressure = 71 Kpa.
Volatility = Highly Volatile.
the existing tank information is ( tank is having external floating roof ) ( API 650 design tank )
tank diameter = 72 meter
tank height = 22.3 meter. refer tank data sheet for more details.
end user require this tank to be use for large cargo loading / unloading operation. flow rate for ship loading & ship unloading operation is change from 5000 m3 / hr to 12000 m3 / hr. because of this change in flow rate , there will be change in tank venting rate ( inbreathing / out breathing ) , no & size of vents, inlet diffuser etc.
I have question how to size inlet diffuser for this new requirement . what sort of modification is require in existing inlet diffuser & tank PVRV valves, sizes in order to comply with end user requirement. is there any other modification need to be done in the storage tank ?
your advice or suggestion is highly helpful to me in presenting the technical proposal to the client.
Note- any other alternative solution to cater above requirement is also welcomed. For doing above modification works in the tank require emptying, gas freeing, sludge removal operation which is time consuming process .
Thanks in advance for the technical advice.
regards
VP