I got a mach number at PSV outlet nozzle = 1 but 0,7 at pipe outlet.
It is ok ?
Thank you
|
Posted 14 November 2017 - 10:18 AM
Hi All,
I got a mach number at PSV outlet nozzle = 1 but 0,7 at pipe outlet.
It is ok ?
Thank you
Posted 14 November 2017 - 11:53 AM
We have no idea what you are doing. Maybe you can provide some information so we might help.
Bobby
Posted 14 November 2017 - 12:08 PM
Dear Mr. Bobby,
API recommend to limit mach number of pipe oulet to 0,7 but it does not talk about PSV outlet nozzle.
I am checking an existing PSV, and I got a Mach Number at PSV outlet nozzle = 1.
Posted 14 November 2017 - 12:41 PM
I got a mach number at PSV outlet nozzle = 1 but 0,7 at pipe outlet.
It is ok ?
Kachisa,
It could be possible in critical flow through the PSV means having sonic flow in PSV orifice which will result in a subsonic flow through the relevant tail pipe due to the back pressure...
Posted 14 November 2017 - 12:47 PM
Thanks Mr. Fallah for your comment.
I got clearly your idea and I totally agree with you.
My worry is not the result, it is rather sound criteria.
Another point : the PSV is sized only for fire case.
As fire flowrate is very important, I will use 2 PSV.
My question is : if these PSV should be staggered ?
I see that is not necessary.
Posted 14 November 2017 - 12:53 PM
Thanks Mr. Fallah for your comment.
I got clearly your idea and I totally agree with you.
My worry is not the result, it is rather sound criteria.
Another point : the PSV is sized only for fire case.
As fire flowrate is very important, I will use 2 PSV.
My question is : if these PSV should be staggered ?
I see that is not necessary.
If you have to use multiple PSV's to handle the whole relif load they should be staggered.either in fire case or in another case...
Posted 14 November 2017 - 01:01 PM
If you have to use multiple PSV's to handle the whole relif load they should be staggered.either in fire case or in another case...
Thanks Mr. Fallah,
2 PSV in service : 1 PSV * 100% + 1 PSV * 105 %
How about the spare PSV, it is set at 100% or 105%, and why ?
Posted 14 November 2017 - 01:11 PM
2 PSV in service : 1 PSV * 100% + 1 PSV * 105 %
How about the spare PSV, it is set at 100% or 105%, and why ?
Spare PSV should be set same as the main PSV...because it's not intended to be operated simultaneous with the main PSV ..
Posted 14 November 2017 - 02:48 PM
Thank you Mr. Fallah,
But PSV 105% may fail ? It is a recommendation from API ?
Posted 15 November 2017 - 01:27 AM
But PSV 105% may fail ? It is a recommendation from API ?
Your statement isn't clear; please explain...
Posted 15 November 2017 - 09:25 AM
For Fire Case PSV, it is not necessary to install spare PSV.
Answered
Nozzle Sizing CalculationStarted by Guest_BabRafiq1_* , 26 Aug 2022 |
|
|
||
Maximum Nozzle Size In The Api 650 TankStarted by Guest_rudiawan_* , 18 Oct 2023 |
|
|
||
Nozzle Sizing In SeparatorsStarted by Guest_krishnamurthy_* , 30 May 2023 |
|
|
||
Answered
Residence Time Dependence On Vessel Outlet NozzleStarted by Guest_lavlysuresh@outlook.com_* , 22 Mar 2023 |
|
|
||
How Does Manufacturers Determine Pump Nozzle SizesStarted by Guest_go-fish_* , 20 Mar 2023 |
|
|