Hello Guys,
My client design a skid in which they discharge PSV into another pipe that already installed with two PSV. I dont think its a good
engineering practice to vent relief pressure into the piping system. What you guys think?
Summary:
"PSV-1002 is meant to release vapour fluid when the system between ESDV-1000 and P-1000 is blocked and thermal expansion (or fire) occurs and the expansion bottle is empty and hence the PSV will release into an empty "vessel". Since thermal expansion is a low volume release the expansion bottle (if empty) is sufficient to contain the release and avoid release into the environment. In the event of a fire, and the expansion bottle full, PSV-1002 will release into a full fluid and hence cause PSV-1000 and 1001 to release.
According to API 521 it is not recommended to have restrictions downstream of a PSV and it is not allowed to have a PSV release into another PSV.Please confirm??