Push button at 15 m is to be provided, so that fuel source could be isolated from a safe distance in field.
Further there can be different schemes for both DCS & field switches, for example, as per MB Lal committee recommendations (India)-
"The first body valve on the tank should be Remote Operated Shut OffValve (ROSOV) on the tank nozzle inside the dyke with Remote Operation only from outside the dyke as well as from the control room. ROSOV should be fail safe and fire safe. It should have only 'close' feature and not 'open' and 'stop' from control room. However, it should have 'close', 'open'& 'stop' operation from the panel located outside the dyke"