Flare Load Upon Instrument Air Failure


4 replies to this topic
Share this topic:
| More

#1 SawsanAli311

SawsanAli311

    Gold Member

  • Members
  • 99 posts

Posted 22 November 2019 - 12:21 PM

Dear All,

 

Based on API 521 6th edition section 5.3.3, a common mode failure such as instrument air can have coincident opening of the emergency depressuring normally energized valves along with the pressure control valves installed across the plant which fail in open position upon loss of instrument air. I know that we can avoid the opening of the BDVs by providing sufficiently sized secured instrument air bottles. However, do we really have to consider or check the above case while designing the flare system? Will the basis of the fact that the starting pressure under the instrument air failure scenario would be relatively lower than the usual conservative basis of relief or emergency fire blowdown design calculations and hence the combined PCV + depressurization load would be hence covered? Do we also have to check the case of all PCVs opening simultaneously to flare across the entire plant? 

 

Thanks 



#2 Pilesar

Pilesar

    Gold Member

  • Members
  • 1,347 posts

Posted 22 November 2019 - 09:38 PM

You must identify all possible causes of overpressure, determine if they are credible, and document them. Each credible scenario must be accounted for when sizing the relief system. If it is a credible case that all PCVs would open simultaneously to flare across the entire plant, then the relief system must be sized for that.



#3 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,930 posts

Posted 28 November 2019 - 09:43 AM

 

Based on API 521 6th edition section 5.3.3, a common mode failure such as instrument air can have coincident opening of the emergency depressuring normally energized valves along with the pressure control valves installed across the plant which fail in open position upon loss of instrument air. I know that we can avoid the opening of the BDVs by providing sufficiently sized secured instrument air bottles. However, do we really have to consider or check the above case while designing the flare system? Will the basis of the fact that the starting pressure under the instrument air failure scenario would be relatively lower than the usual conservative basis of relief or emergency fire blowdown design calculations and hence the combined PCV + depressurization load would be hence covered? Do we also have to check the case of all PCVs opening simultaneously to flare across the entire plant? 

 

 

Hi,

 

IA failure is one of common failure among other ones, hence the total relief load upon IA failure should be brought into flare load summary to evaluate the governing case for flare header and stack sizing. Then no matter the relieving fluids following to IA failure are due to BDV or PCV opening individually or simultaneously...



#4 usaidsaif

usaidsaif

    Brand New Member

  • Members
  • 3 posts

Posted 03 April 2020 - 01:59 PM

i am trying to post this as a new topic but its not working.sorry to include here

 

 

Hello.i have a question.in a ptoject  some part of flare header is of mixed material.cs and ss
In  ss tie ins are bascially from hcdp unit wheres tempersture ranges are below -50f
First 600 m is of ss.now client want me to tie in ss and tell him that till what length temperture shall be positive so that it doesnt effect it cs portion.
How i can check that till what length my negative temp -60f which i have tie in ss will be in positive temp so that it doesnt effect cs portion



#5 SawsanAli311

SawsanAli311

    Gold Member

  • Members
  • 99 posts

Posted 05 April 2020 - 01:08 PM

You need to do a heat transfer pick up calculation (you can use HYSYS) to estimate the minimum straight length required to allow heat pick up from ambient. However, be cautious for considering a conservative air velocity (based on historical data). Also, note that you need to account for the pressure drop requirements because of straight length as well as any expansion loops. 