Does A Level Troll Shows 0% Level When Vessel Is Completely Filled Wit


3 replies to this topic
Share this topic:
| More

#1 muthukmaar

muthukmaar

    Gold Member

  • Members
  • 53 posts

Posted 12 August 2020 - 12:01 AM

In our Absorber we have an Level Troll and another Level transmitter of Differential pressure type. When the vessel is full the Differential pressure transmitter shows 0% level since both it's legs are filled with solution.
Why doesn't the level troll also shows similar reading

#2 breizh

breizh

    Gold Member

  • Admin
  • 6,339 posts

Posted 12 August 2020 - 12:22 AM

Hi,

Talk to your E&I engineer to investigate the cause ! 

It's a field problem I believe.

Good luck

Breizh 



#3 Lincon

Lincon

    Brand New Member

  • Members
  • 1 posts

Posted 16 August 2020 - 10:15 AM

The level troll is vented to atmosphere whereas the dpt apparently has both sides liquid filled. You might want to re-evaluate the placement of the dpt so the both the inlet and outlet legs are not seeing the full liquid column. Make sure the upper leg is in the vapor space and you will see a differential.

#4 breizh

breizh

    Gold Member

  • Admin
  • 6,339 posts

Posted 16 August 2020 - 09:56 PM

Hi

Is it a new problem or from start up ? 

Please review the doc attached for better understanding about the technology. 

The LP leg should be connected to the gas head space . If you are worried about condensation , you could use a capillary which means totally sealed .

Did you talk to your vendor ?

Breizh 