Closed Cooling Water System Balancing Valve Preferred Location ?
#1
Posted 14 July 2022 - 01:18 PM
I am considering to locate the balancing valve on the supply as I intend to make the isolation valve on the return as locked open to provide an open path to a PSV on the expansion drum for a relief scenario.
#2
Posted 14 July 2022 - 02:33 PM
A relief valve on each exchanger is probably less costly than a lock open valve. And you won't have to monitor the valve. It sounds as if this is a small system. Otherwise you would use direct air intercoolers.
Bobby
#3
Posted 14 July 2022 - 03:08 PM
Just curious why would a PSV be less expensive than LO valve?
I do not want to digress this topic towards overpressure protection but if we set aside LO valve and point to main query look, is there a preferred location of the manual balancing valve? These should be just set once during commissioning and start-up based on the design flow.
#4
Posted 14 July 2022 - 03:56 PM
What you are going to find for a tube rupture case is a tremendous relief rate. Because all the liquid must accelerate the required pressure will be much greater than 11 bar. It's unlikely that 11 bar is high enough in this instance. If this is a small system, a double pipe exchanger will eliminate the need for overpressure protection resulting from a tube rupture.
Bobby
Edited by Bobby Strain, 14 July 2022 - 04:39 PM.
#5
Posted 14 July 2022 - 05:10 PM
Anyone, any feedback on the balancing valve location before this thread becomes an overpressure protection focused and I am being told off for not putting this query in the correct forum? ????
#6
Posted 14 July 2022 - 06:42 PM
You need to hire a professional who can conduct a dynamic analysis. The results may show that you need a rupture disk on the heat exchanger. The usual steady state analysis is not sufficient.
Bobby
Similar Topics
Can Anyone Provide Me The Reference Datasheet For Deluge Valve?Started by Guest_Radha Krishnan Siva Kumar_* , 16 Apr 2024 |
|
|
||
Waste WaterStarted by Guest_refluxraider_* , 14 Apr 2024 |
|
|
||
Water Seal DrumStarted by Guest_Ali4269278331_* , 05 Apr 2024 |
|
|
||
Handling The Limited Capacity Of Flare SystemStarted by Guest__1angelia23_* , 05 Apr 2024 |
|
|
||
Closed Drain SystemStarted by Guest_Falah_* , 26 Mar 2024 |
|
|