hi, all
There are three types(class 1/2/3) of igniters in NFPA85.
Where Class 1 igniters are provided, the main burner flame shall be proven either by the flame detector or by the igniter being proven.
Burners with Class 2 igniters shall have at least two flame detectors.
Burners with Class 3 igniters shall have at least one flame detector.
why the requirement of Class 3 is lower than Class 2?