Bulk Storage Of Dichloromethane
Started by amaity, Jan 03 2009 09:42 PM
1 reply to this topic
Share this topic:
#1
Posted 03 January 2009 - 09:42 PM
Hello and Happy New Year to everybody.
I have some questions about bulk storage of Dichloromethane (M.W. = 84.93, Boiling pt. = 39.8 degC).
What is the operating temperature and pressure of the storage tank for Dichloromethane?
What kind of arrangement is provided to prevent the vapour losses?
How is Dichloromethane transported in bulk quantities? Is it transported at a lower temperature?
Best regards
amaity
I have some questions about bulk storage of Dichloromethane (M.W. = 84.93, Boiling pt. = 39.8 degC).
What is the operating temperature and pressure of the storage tank for Dichloromethane?
What kind of arrangement is provided to prevent the vapour losses?
How is Dichloromethane transported in bulk quantities? Is it transported at a lower temperature?
Best regards
amaity
#2
Posted 06 July 2011 - 01:56 AM
Dear Amaity,
As we all know B.Pt of DCM is 39.8°C, it must be stored in temerature below to its boiling point. Also if the Location of Tank installed is having room temperature more than 35°C, it is adviseable to provide a insulated layer on the tank to prevent heat transfer. installation of a vent condenser with chilled water circulation will reduce DCM Losses. Jacketed Tank with cooling water circulation is also good option.
Safety devices may could include, HIgh and Low Level Alarm System, Breather valve Installation. Although DCM is not flameable but if flame arrestor is
installed before breather valve, plz note that MOC should be SS-304. Testing of Breather valve on regular intervals is also important to prevent pressurization of tank. DCM Storage should be done under atmospheric condition and after fabrication of Tank, Pressure testing should be done.
Hope the given information be beneficial to you.
Regards
Sahil
As we all know B.Pt of DCM is 39.8°C, it must be stored in temerature below to its boiling point. Also if the Location of Tank installed is having room temperature more than 35°C, it is adviseable to provide a insulated layer on the tank to prevent heat transfer. installation of a vent condenser with chilled water circulation will reduce DCM Losses. Jacketed Tank with cooling water circulation is also good option.
Safety devices may could include, HIgh and Low Level Alarm System, Breather valve Installation. Although DCM is not flameable but if flame arrestor is
installed before breather valve, plz note that MOC should be SS-304. Testing of Breather valve on regular intervals is also important to prevent pressurization of tank. DCM Storage should be done under atmospheric condition and after fabrication of Tank, Pressure testing should be done.
Hope the given information be beneficial to you.
Regards
Sahil
Hello and Happy New Year to everybody.
I have some questions about bulk storage of Dichloromethane (M.W. = 84.93, Boiling pt. = 39.8 degC).
What is the operating temperature and pressure of the storage tank for Dichloromethane?
What kind of arrangement is provided to prevent the vapour losses?
How is Dichloromethane transported in bulk quantities? Is it transported at a lower temperature?
Best regards
amaity
Similar Topics
Sulphuric Acid H2So4 Storage TankStarted by Guest_TeeEng_* , 08 Apr 2024 |
|
|
||
Butadiene StorageStarted by Guest_Mirzazada_* , 27 Mar 2021 |
|
|
||
Green Diesel StorageStarted by Guest_Lucianaa_* , 16 Feb 2024 |
|
|
||
Determination Of The Number Of Foam Chambers For Storage TanksStarted by Guest_AnbIran_* , 15 Feb 2024 |
|
|
||
Crude Oil Storage CapacityStarted by Guest_Noman97_* , 19 Jan 2024 |
|
|