It is a practise in our facility that whenever there is a gas leak from a flange,a steam hose is applied to the point of leak. The reason provided is to dilute the gas.
The gas is ethylene at 100 to 300 barg.
Any comments on this? Do any of you use any other method to mitigate online HC leaks in the plant.
AFD
|

Gas Leak
Started by Guest_Guest_afdmello_*_*, Dec 10 2005 01:23 PM
3 replies to this topic
Share this topic:
#1
Guest_Guest_afdmello_*_*
Posted 10 December 2005 - 01:23 PM
#2
Posted 12 December 2005 - 06:21 AM
Basically, what you describe is some simple, mobile form of a "steam curtain". Other methods used are fixed steam curtains and mobile or fixed water curtains. Water curtains can be provided using either spray nozzles or water monitors.
Purpose of all these systems is to generate some air flow in order to move and dilute the flammable gas. Preferably they are located as close as possible to the potential leak sources (flanges), but sometimes they are also employed in front of potential ignition sources (e.g. fired heaters).
An example of a steam curtain used in an ethylene plant to prevent ignition of a flammable gas cloud by the cracking heaters is given in the following link (see picture 3): http://www.basf.de/e...3LQ1w7s9Qbsf3kt
Purpose of all these systems is to generate some air flow in order to move and dilute the flammable gas. Preferably they are located as close as possible to the potential leak sources (flanges), but sometimes they are also employed in front of potential ignition sources (e.g. fired heaters).
An example of a steam curtain used in an ethylene plant to prevent ignition of a flammable gas cloud by the cracking heaters is given in the following link (see picture 3): http://www.basf.de/e...3LQ1w7s9Qbsf3kt
#3
Guest_Guest_afdmello_*_*
Posted 12 December 2005 - 02:11 PM
Gvdlans,
I was thinking on the static charge that can build,as steam and ethylene are static charge generators.Is nitrogen not a better tool to dilute and disperse the HC.
AFD
I was thinking on the static charge that can build,as steam and ethylene are static charge generators.Is nitrogen not a better tool to dilute and disperse the HC.
AFD
#4
Posted 13 December 2005 - 04:14 AM
You can and have to prevent static charges by proper grounding and bonding.
Nitrogen will not always be present in sufficient quantities and has its own safety issues (asphyxiation).
Nitrogen will not always be present in sufficient quantities and has its own safety issues (asphyxiation).
Similar Topics
![]() Nitrogen Leak Test On PipeStarted by Guest_mesbah_* , 24 Oct 2024 |
|
![]() |
||
Ethylene Tanks Cctv For Leak DetectionStarted by Guest_DarthJamming_* , 30 May 2024 |
|
![]() |
||
P&id Marking Up For The Leak TestStarted by Guest_JKM_* , 04 Jan 2023 |
|
![]() |
||
Fuel Gas Piping Leak TestStarted by Guest_CSNK_* , 23 Aug 2021 |
|
![]() |
||
Nitrogen Leak TestStarted by Guest_Danish John Paul_* , 31 Aug 2021 |
|
![]() |