Tube side (water) : 31.6 kgf/cm2 g * (operating 21 kgf/cm2 g).
Shell side (gasoil) : 14 kgf/cm2 g * (operating 10 kgf/cm2 g).
* same for upstream / downstream piping.
Note: Certified hydrostatic test pressure of shell side : 21 kgf/cm2 g
According to API 521 (para 5.19: heat transfer equipment failure) “complete tube rupture is a remote but possible contingency” in this case. This could be cured by pressure relief on the shell side or connected vicinity piping. Nevertheless “the tube rupture scenario can be mitigated by assuring that an open flow path can pass the tube rupture flow without exceeding the stipulated pressure”.
Gasoil circuit is shown on the attached diagram. Downstream exchanger, gasoil passes from an air cooler and a LCV (level control valve) interlocked with the crude tower side, then ends to storage. There are also a lot of manual valves along the way, none of them locked open.
Suppose that a tube rupture occurs suddenly under normal operating conditions, and there is no LCV installed. Water flows with gasoline to storage, and resulting ΔP is not high enough to create overpressure, as long as all manual valves remain open. Can we avoid PRV installation, considering the above line as an open flow path? According to a vew closing a manual valve would make a double contingency.
Now suppose the previous event, but with the LCV already installed on the line. Its opening depends on Level in the Crude Distillation Tower, not affected by tube rupture. Can the line be considered as an open flow path?
Advise on the point and the questions would be appreciated.
It is pointed out that tube operating pressure exceeds shell design pressure.