Resizing Existing Psv Discharge Lines
#1
Posted 11 May 2010 - 12:28 PM
THis is when I ran into problems. I'm probably complicating the solution more than I need to but API mentioned that the velocity at the discharge of the valve would increase until the sonic velocity is reached. Should I be using this instead as my built up back pressure? Any information about the proper way to size discharge piping (including header sizing for several PSV discharges combining) would be appriciated. I do have and will be using the rated discharge capacity of the valves as my flowrate.
#2
Posted 13 May 2010 - 07:40 AM
By the way, relieving pressure = set pressure + overpressure = design pressure (or MAWP) + accumulation (see the definitions on API 520 & 521) and the criteria to size the outlet line of a PSV in based on a percentage of SET PRESSURE not relieving pressure.
Once you have sized and selected a standard PSV nozzle, then you know the rated discharge flowrate and can size the inlet and outlet line. If you consider that the % blowdown is usually 6% and that the % overpressure is usually 10% (except when the sizing scenario is fire and where ASME code is applicable), then you size the inlet line for frictionnal pressure drop less than 3% (half the blowdown) of the set pressure and the outlet line for frictionnal pressure drop less than 10% (the overpressure) of the set pressure.
Usually there is also a Mach number limitation on the discharge line, maximum Mach 0.7 as far as i remember.
Again, refer to API for the correct definitons and criteria.
#3
Posted 13 May 2010 - 08:05 AM
I'm probably complicating the solution more than I need to but API mentioned that the velocity at the discharge of the valve would increase until the sonic velocity is reached. Should I be using this instead as my built up back pressure? Any information about the proper way to size discharge piping (including header sizing for several PSV discharges combining) would be appriciated. I do have and will be using the rated discharge capacity of the valves as my flowrate.
What you should consider in discharge line sizing is "the pressure just downstream of the PSV nozzle shall be equal/less than 10% of the set pressure" and the way of proper sizing,usually done based on back calculation from end of discharge line,would be available in API 521 and similar sources.
Depending on piping configuration,pipe size,reducer size,relif flowrate,....you may have several choked point along the discharge line.
#4
Posted 13 May 2010 - 08:22 AM
What you should consider in discharge line sizing is "the pressure just downstream of the PSV nozzle shall be equal/less than 10% of the set pressure" and the way of proper sizing,usually done based on back calculation from end of discharge line,would be available in API 521 and similar
Dear Fallah
The pressure you define is indeed the total backpressure, while API apply the sizing criteria to built-up backpresure for conventionnal PSV.
For the OP: total backpressure = built-up backpressure (frictionnal pressure drop on the line due to PSV discharge) + superimposed backpressure (pressure before PSV dicharges)
Edited by sheiko, 16 May 2010 - 03:22 PM.
#5
Posted 13 May 2010 - 11:40 AM
Dear Fallah
The pressure you define is indeed the total backpressure, while API apply the sizing criteria to built-up backpresure for conventionnal PSV.
For the OP: total backpressure = built-up backpressure (frictionnal pressure drop on the line due to PSV discharge) + superimposed backpressure (pressure before PSV dicharge)
Dear Sheiko,
The pressure i mentioned,is the build-up back pressure.Superimposed back pressure is supposed being already considered in PSV spring adjustment.
#6
Posted 13 May 2010 - 12:27 PM
I regret but the pressure at the PSV nozzle outlet flange is always the TOTAL backpressure when the PSV is dicharging.Dear Sheiko,
The pressure i mentioned,is the build-up back pressure.Superimposed back pressure is supposed being already considered in PSV spring adjustment.
#7
Posted 13 May 2010 - 01:24 PM
I regret but the pressure at the PSV nozzle outlet flange is always the TOTAL backpressure when the PSV is dicharging.
You are right and as i mentioned i meant build-up back pressure at the PSV outlet flange shouldn't be more than 10% of PSV set pressure.
#8
Posted 13 May 2010 - 04:17 PM
Alright it is clearer then.
#9
Posted 25 November 2010 - 09:06 AM
what we should consider for discharge line sizing is 10% rule and mach number (<0.7). I agree on that. My problem is, when the discharge fluid (from relief valve outlet) goes to common flare header, it's easy to apply above two rules. Yet, if the discharge fluid goes directly into atmospheric venting (which is very short line), then they will have their own problem. Pressure difference between relief valve outlet and vent pipe outlet would be too huge, this will lead into very high velocity in discharge piping (300-500ft/s). The built-up back pressure would also be quite high since the discharge line is very short. I'm kind of bit missing something here. please help guys...
thank you
#10
Posted 25 November 2010 - 01:31 PM
In general,short tailpipes terminated to atmosphere result in lower build up back pressure than long PSV outlet line.
If choked flow occurs at the outlet of a short tailpipe vented to atmosphere,high build up back pressure would be establshed.
Regards
#11
Posted 26 November 2010 - 12:30 AM
sorry if my question seems odd for you since I'm a newbie to relief system.
you said that, "In general,short tailpipes terminated to atmosphere result in lower build up back pressure than long PSV outlet line." Could you please explain in a more detail way? Is this something to do with built-up back pressure? When the K value and f*L/D value are high, the discharge line pressure drop will be great. We all know that the built-up back pressure = outlet vent pipe + discharge line pressure drop. Therefore, if the pressure drop along the discharge line is great, then the built-up back pressure would be low. Is my understanding correct? please advice
"If choked flow occurs at the outlet of a short tailpipe vented to atmosphere,high build up back pressure would be established."
So I guess if choked flow occurs, then atmospheric venting would not be a good choice for the discharge line? is this correct?
Is there any rule of thumb for determination of venting pipe sizing and length for atmospheric venting? The discharge line is only consist of small amount horizontal pipe, one long radius elbow as well as vertical pipe (for stack) and the optional weather cap as specified on API 520 partII.
thank you, br
#12
Posted 26 November 2010 - 12:30 AM
sorry if my question seems odd for you since I'm a newbie to relief system.
you said that, "In general,short tailpipes terminated to atmosphere result in lower build up back pressure than long PSV outlet line." Could you please explain in a more detail way? Is this something to do with built-up back pressure? When the K value and f*L/D value are high, the discharge line pressure drop will be great. We all know that the built-up back pressure = outlet vent pipe + discharge line pressure drop. Therefore, if the pressure drop along the discharge line is great, then the built-up back pressure would also be great. Is my understanding correct? please advice
"If choked flow occurs at the outlet of a short tailpipe vented to atmosphere,high build up back pressure would be established."
So I guess if choked flow occurs, then atmospheric venting would not be a good choice for the discharge line unless we choose to employ balanced bellow type or pilot operated relief valve. is this correct?
Is there any rule of thumb for determination of venting pipe sizing and (minimum) length (or height) for atmospheric venting? The discharge line is only consist of small amount horizontal pipe, one long radius elbow as well as vertical pipe (for stack) and the optional weather cap as specified on API 520 part II.
thank you, br
#13
Posted 26 November 2010 - 06:53 AM
Dear Fallah,
sorry if my question seems odd for you since I'm a newbie to relief system.
you said that, "In general,short tailpipes terminated to atmosphere result in lower build up back pressure than long PSV outlet line." Could you please explain in a more detail way? Is this something to do with built-up back pressure? When the K value and f*L/D value are high, the discharge line pressure drop will be great. We all know that the built-up back pressure = outlet vent pipe + discharge line pressure drop. Therefore, if the pressure drop along the discharge line is great, then the built-up back pressure would be low. Is my understanding correct? please advice
Back pressure due to pressure drop in the PSV discharge line when PSV opens named as "Build up Back Pressure".Longer discharge line results in higher pressure drop leading to higher build up back pressure.
"If choked flow occurs at the outlet of a short tailpipe vented to atmosphere,high build up back pressure would be established."
So I guess if choked flow occurs, then atmospheric venting would not be a good choice for the discharge line? is this correct?
Selecting larger valve outlet size,or choosing bellows/pilot operated type may solve the problem
Is there any rule of thumb for determination of venting pipe sizing and length for atmospheric venting? The discharge line is only consist of small amount horizontal pipe, one long radius elbow as well as vertical pipe (for stack) and the optional weather cap as specified on API 520 partII.
It should be evaluated case by case.
thank you, br
#14
Posted 28 November 2010 - 08:52 PM
#15
Posted 10 December 2010 - 10:22 PM
I still have something to discuss with you guys related to the above mentioned atmospheric discharge line. I have simulated a very simple atmospheric discharge line using Aspen Flarenet 2006 and I wanted to attach the '.fnw' file to the forum, but this forum doesn't allow me to attach '.fnw' file or '.rar' file. If anyone knows how to upload my simulation file, please kindly do let me know.
With regard to my flarenet simulation, the situation is like this,
I still have the problem with choked flow. The back pressure is okay, only the Mach number of the stack trouble me. My orifice area of 'T' letter, 8" of inlet and 10" on outlet. Both the tailpipe and stack diameter is 10". Choked Flow occurs at the end of stack. The rest is okay. I used balance bellow valve to accommodate for relative high back pressure.
This choked flow problem will be solved if I increase both the diameter of tailpipe & stack to 24", but then if I do this I will have to put the reducer to connect relief valve outlet (10") with tailpipe (24"). I believe this will lead to another choked flow at relief valve outlet.
My conclusion is I will go with 10" diameter of tailpipe and stack and ignore the occurrence of choked flow at the end of stack. Please advise if I'm wrong.
fyi, the mass flow is 160,000kg/h with set pressure of 15.87 psig. The fluid is saturated steam at 190 C degree.
Thanks in advance my fellow engineers.
regards,
bernath
Attached Files
#16
Posted 25 March 2011 - 12:11 PM
A. As informed by a friend, a preliminary sizing (or size check) of PSVs' discharge network can be:
1. Size the network for fire case, assuming superimposed back pressure = 0.3 kgf/cm2 g. The latter is assumed as operating pressure in the flare header. During fire all the PSVs of a "fire area" are assumed open, but rest PSVs of the factory are assumed idle (factory is divided in several "fire areas" according to criteria by NFPA). This can be repeated for every "fire area", considering one strong fire at a time.
Note: Fire may cause opening of PSVs designed to cover fire, but simultaneously of other PSVs, e.g. for blocked outlet.
2. Size the network for a general power failure case, assuming superimposed back pressure = 1.0 kgf/cm2 g. This because a lot of PSVs from all factory open during a general power failure.
3. Can fire at one "fire area" cause power failure in other areas? "Yes" is a conservative answer. When we check capacity adequacy of a new unit, we also consider the case of fire in this unit and at the same time general power failure in the factory.
4. For every part of network make a conservative size selection between (1) and (3).
5. Start now checking the size of resulting network in detail, for every possible scenario of exceeding flow, to trace any necessary further size increase.
For all above, rule of PSV discharge line delta P and of max mach=0.6-0.7 is applicable. Flarenet is usually applied.
B. Concerning Bernath's recent post, it is understood that pressure upstream flare tip is at least 14.7+1.3=16.0 psia, versus a PSV set pressure of 14.7+15.87=30.57 psig. I do not feel the issue physically; but increasing line sizes (diameters) may transfer the chocked flow at the PSV itself (upstream of reducer), which is not troublesome.
Not having enough background, a way out in this issue by others would be welcomed.
Edited by kkala, 25 March 2011 - 12:22 PM.
#17
Posted 27 March 2011 - 10:25 AM
B. Concerning Bernath's recent post, it is understood that pressure upstream flare tip is at least 14.7+1.3=16.0 psia, versus a PSV set pressure of 14.7+15.87=30.57 psig. I do not feel the issue physically; but increasing line sizes (diameters) may transfer the chocked flow at the PSV itself (upstream of reducer), which is not troublesome.
Not having enough background, a way out in this issue by others would be welcomed.
Yes, please anyone who has the answer for the issue.
It's like transferring the choked flow from the tip to the relief valve outlet. What is the consequences of such act?
I also know that there's 3 mechanisms of choking, i.e. end-point, expansion and restriction choking. The pressure at relief valve outlet will undergo expansion choking while end point choking will occur at flare tip. Which one is most dangerous? Should I put the choke point at flare tip or at relief valve outlet? Which one is better? What is the consequences of each act?
hope someone can help
thank you
regards,
bernath
#18
Posted 28 March 2011 - 11:31 AM
The problem with having choked flow at the flare tip (which means sonic velocity) is that unless the flare tip has been specially designed for sonic flow, the flame will lift off and you will have an unignited discharge, which is dangerous. This is the reason why it is general practice to limit the velocity at a pipe flare tip to about 0.5 to 0.7 Mach.(as well as to limit noise).
It is not uncommon to have choked flow at the PSV discharge flange. Immediately downstream of the discharge flange (even before any isolation valve) should be a pipe expander to fit the tailpipe, which should be sized for 0.7 Mach approx, often much larger than the discharge flange. If you have choked flow where the tailpipe joins the header then the tailpipe is too small. High velocity at this point can give rise to vibrations which can result in fracture of the joint into the header, I have seen photos where this has happened.
You need to get an expert to check the acoustic vibration energy in this tailpipe.
Paul
#19
Posted 28 March 2011 - 09:24 PM
Bernath,
The problem with having choked flow at the flare tip (which means sonic velocity) is that unless the flare tip has been specially designed for sonic flow, the flame will lift off and you will have an unignited discharge, which is dangerous. This is the reason why it is general practice to limit the velocity at a pipe flare tip to about 0.5 to 0.7 Mach.(as well as to limit noise).
It is not uncommon to have choked flow at the PSV discharge flange. Immediately downstream of the discharge flange (even before any isolation valve) should be a pipe expander to fit the tailpipe, which should be sized for 0.7 Mach approx, often much larger than the discharge flange. If you have choked flow where the tailpipe joins the header then the tailpipe is too small. High velocity at this point can give rise to vibrations which can result in fracture of the joint into the header, I have seen photos where this has happened.
You need to get an expert to check the acoustic vibration energy in this tailpipe.
Paul
Hi Paul,
Thank you for such a nice answer. The way you describe your answer is simply wonderful.
bernath
Similar Topics
Physical Properties Of Liquid Discharge For Kod SizingStarted by Guest_mahmooddalvi09_* , 26 Feb 2025 |
|
![]() |
||
![]() How To Replace Existing Reboiler With A Thermosyphon Reboiler In HysysStarted by Guest_tomr91_* , 04 Feb 2025 |
|
![]() |
||
Recip Compressor Discharge PrvsStarted by Guest_go-fish_* , 15 Oct 2022 |
|
![]() |
||
![]() Discharge Head Or Differential Head, Pump CurveStarted by Guest_panoska_* , 11 Nov 2024 |
|
![]() |
||
![]() Positive Displacement Pump Psv Discharge LocationStarted by Guest_QuantumEng_* , 24 Jul 2024 |
|
![]() |