(α) Oily water feed from tank roof, through one existing 12 vertical guide-pall (whose holes shall be plugged and instruments shifted). Discharge line (10) shall be connected to it.
(β) Effective siphon break, through an open pipe / vent of proper height, connected to the highest part of the feeding pipe line (see siphonbrake.xls).
Note: Their practice for siphon break concerning cone roof tanks is to make some holes on the vertical feeding line between cone roof and high high liquid level (not applicable to floating roof tank).
Β. Briefly looking into requirements, following drawbacks have been understood:
(1) Assuming all discharge pipe full of liquid up to the exit, pressure at highest part of line (feeding the tank) is below atmospheric at any flow rate. If an open vent is installed, this would cause air ingression into the guide-pall (dangerous). Referring to siphonbrake.xls diagram, mentioned pressure is calculated to:
For tank full of crude (sg = 0.84): 22.5/10*0.84- 25/10*1.0 = -0.61 kp/cm2 g .
For tank full of water: 22.5/10*1.0 - 25/10*1.0 = - 0.25 kp.cm2 g
For liquid at LLLL : 2/10*1.0 25/10*1.0 = - 2.3 kp/cm2 g (impossible)
Note: Frictional ΔP in 12 guide-pal is neglected, as insignificant (0.06 kp/cm2 at 600 m3/h). Static pressure cannot balance frictional pressure drop in the flow range 50-600 m3/h. I imagine flow in the guide-pall is not full. But on what criterion is this based on? End of curve data of existing 2x50 m3/h pumps is 2x 90 m3/h at 31 m of liquid, no such data available for the pump of 600 m3/h.
(2) In the (improbable) case of plugged guide pall, pump shall develop its shutoff pressure, so level in the open pipe will be rised by h = 45-27 = 18 m in case of 50 m3/h pumps operating (probably higher if the 600 m3/h pump operates).
Note: Frictional pressure drop of 10 discharge line to its highest point is calculated to 1.3 kp/cm2 for 600 m3/h flow rate. Assuming an open vent of h=0 m at mentioned point, pressure at pump discharge is 27/10*1.0+1.3 = 4.0 kg/cm2 g, that is 40 m of liquid. But if there is no open vent at the highest point, what is the pressure required at the pump discharge? (see siphonbrake.xls, 600 m3/h).
C. After the above considerations, the possibility of elevating the 10 discharge pipe (feeding the tank) 12 m over tank HHLL is investigated, that is 10 m over tank peripheral wall. This could prevent back flow from tank to (oily) water, seeing that siphon cannot be maintained if height difference exceeds 10 m for water or 10/0.84~11.9 m for crude. And flow patern in guide-pall may be forgotten in this case. However this pipe elevation will be probably not acceptable by statuary authorities for permit.
D. We will try to convince Client that 280 m3/h of flow rate covers the max rainfall (which will reduce discharge pipe size to 8), yet problem will actually remain. Any comments on above or advice on the matter or proposal would be highly appreciated. Probably someone has faced a similar situation, or my inexperience on downward flow complicates the issue. Some siphon breaks (sensing flow direction) have been seen in WWW, but their reliability is not known. Or probably flow arrangement has to be modified (e.g. control valve?) to give a satisfactory solution.