Hello all,
As per API 521 2007, section 5.20.1, it recommends that reducing the equipment pressure from initial conditions to a level equivalent to 50% of the vessels design pressure within approximately 15 min. This criterion is based on thickness of approximately 1 in or more. Vessel with thinner walls generally require a somewhat faster depressurizing rate. The required depressurizing rate depends on the metallurgy of the vessel, the thickness and initial temperature of the vessel wall and the rate of heat input. API also figures out an example for Grade 70, but it quite confuses me to determine maximum allowable required depressurizing time.
My question is that how to ensure the selected depressurizing time is suitable. This is to ensure vessel shall not be rupture before completion of depressurizing.
- How to determine the temperature of vessel causing by fire to be referred for benchmark at Figure 2 - page 39. (API classify 1000, 1200, 1300, 1400)?
- How to determine the rupture stress of vessel material (note Grade 70)
Posted 27 March 2012 - 08:43 PM
Posted 28 March 2012 - 02:28 AM
eastorka,
Normally, for each 5 mm decrease in thickness (from 25 mm) 3 minutes is subtracted from 15 minutes and this time would be applied as depressurizing time for thinner wall vessel.
Fallah
Posted 29 March 2012 - 01:37 AM
Fallah,
Interesting basis but where it came from or is it rule ofthumb?
Posted 29 March 2012 - 01:52 AM
Aj,
It is from engineering practice which we are using in our "gas refinery" projects.
Fallah
Fallah
Posted 29 March 2012 - 03:42 AM
Thanks and if you dont mind can you share that with us?
rgds,
Aj
rgds,
Aj
Surface Area Calculation For Blowdown Orifice Sizing Including FinnedStarted by Guest_victortheone_* , 17 Feb 2026 |
Automatic Choke ValveStarted by Guest_Mudassssir011_* , 22 Jul 2025 |
Steam Flow And Heating Time In Batch ReactorStarted by Guest_seagal6_* , 16 Jul 2025 |
What Can I Do With My Leftover Time In UniversityStarted by Guest_Acetimeter_* , 25 Jun 2025 |