Need Set Pressure To In/out-Breathing,emergency Relief Of Storage Tank


This topic has been archived. This means that you cannot reply to this topic.
12 replies to this topic
Share this topic:
| More

#1 Phukan

Phukan

    Junior Member

  • Members
  • 19 posts

Posted 20 September 2012 - 11:15 AM

Hi everyone,

We are in a process of changing a floating roof tank to floating cum fixed used for storage of hexane(food grade). Tank dia:20m H: 9.6 m. The tank will is nitrogen blanketed. I wanted to know what will be the in/out breathing set pressure and relief pressure. Following parameters are known:
Design pressure: full of water with nitrogen blanketing with 50 mm WC.
Vapor pressure of hexane(98% purity at 40 deg cel)) to be 400mbara,
Cut point : 63-70 Deg cel.
I have calculated the flowrates for in/out breathing as per API 2000 but I cant seem to find a way to set the trigger pressure.

Kindly help

#2 proinwv

proinwv

    Gold Member

  • ChE Plus Subscriber
  • 391 posts

Posted 20 September 2012 - 01:43 PM

You need to map out the pressure profile of your tank using the operating bands of all devices and avoid interaction of devices while keeping the entire profile within the MAWP and MAWV of the tank.

The standard cannot do this for you. Each situation is unique.

#3 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 5,019 posts

Posted 23 September 2012 - 03:47 AM

Phukan,

As Paul well explained don't worry about the set point value determination; it should be set such that just there would be no interaction between adjacent devices and be within MAWP and MAWV of the tank. In this way be noted that saving the blanketing gas consumption due to lowering the set point is very small.

Fallah

#4 proinwv

proinwv

    Gold Member

  • ChE Plus Subscriber
  • 391 posts

Posted 23 September 2012 - 03:41 PM

But keep in mind that careful attention must be paid to the operating band of the blanketing valve and the vacuum vent. With very low setpoints beware of passing into negative pressures and opening the vacuum vent which will allow atmospheric air to enter the tank. While gas is saved by operating at lower pressures, it is a function of the ratio of absolute pressures.

#5 DB Shah

DB Shah

    Gold Member

  • ChE Plus Subscriber
  • 156 posts

Posted 26 September 2012 - 06:03 AM

I normally prefer @ 25 to 50% margin between each setting.

Typical case-
Tank design pressure = say 300 mmWCg
ERV (fire case,hatch) opens above 200 mmWCg 300/200 ~ 50% margin
Breath out valve opens above 150 mmWCg 200/150 ~ 33% margin
N2 Blanketing valve closes above 100 mmWCg 150/100 50% margin -- maximize this margin to minimize inert into tank
N2 Blanketing valve opens below 100 mmWCg
Breath in opens at & below -25 mmWCg
Tank design pressure (negative side) -50 mm

#6 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 5,019 posts

Posted 26 September 2012 - 07:44 AM

I normally prefer @ 25 to 50% margin between each setting.


DB Shah,

It should be noted that the margin between each two settings should be included both of dead band margin (to prevent interacting) and operating margin (overpressure, blowdown, lock-up pressure, droop pressure,....). Hence, there isn't a prespecified range by which the margins between settings are to be adjusted and each case should be investigared as per its own design information. As a sample, you consider tank design pressure/vacuum equal to 50 mmWCg/-5mmWCg and try to set all devices between these two values.

Fallah

Edited by fallah, 26 September 2012 - 08:02 AM.


#7 proinwv

proinwv

    Gold Member

  • ChE Plus Subscriber
  • 391 posts

Posted 26 September 2012 - 06:09 PM

and you will need to contact the hardware manufacturers to obtain the operating band for the devices.

#8 Phukan

Phukan

    Junior Member

  • Members
  • 19 posts

Posted 27 September 2012 - 02:07 AM

Thank you all for your valued suggestions. I always learn a lot whenever I log in to this forum.

#9 hos2244

hos2244

    Brand New Member

  • Members
  • 2 posts

Posted 19 February 2013 - 10:01 AM

Dear Sirs,



Your recommendations were also somehow useful to us but we have a
problem similar to Mr. Phukan's problem.



An Old Fixed Cone Roof Tank filling with LPG and blanketing gas. The Diameter
is 20m and 15 Height. The Tank is over 30 years old and its PVSV is out of use.



I'm responsible to determine the exact set point of Vacuum/Positive
Pressure to buy a New one. For that, we have tried to obtain the MAWP of the
Tank during filling or suddenly draining the Tank. The obtained values are
mentioned below:



Vacuum: -0.03 psig



Positive Pressure: +0.35 psig



At these values, the Tank started to have dangerous vibrations. Could you
please let me know the way to use these values to pass the responsibility? Or is
there any relation between these values and the set point of the PVSV?



Thanks



Ghaffari



#10 proinwv

proinwv

    Gold Member

  • ChE Plus Subscriber
  • 391 posts

Posted 19 February 2013 - 01:37 PM

Sir, your test reveals some significant structural issues with the tank at relatively low pressures. Certainly you could not operate anywhere near these points. If I were asked to place a system on such a tank that results in the tank operating at pressure and vacuum, I would refuse.

 

Paul



#11 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 5,019 posts

Posted 20 February 2013 - 01:41 AM

Hi,

 

As Paul rightly stated, not only the tank's PVSV is out of use but also appears the tank itself should be put aside... 



#12 hos2244

hos2244

    Brand New Member

  • Members
  • 2 posts

Posted 22 February 2013 - 01:08 PM

Hi,

Thanks for your help. I'll try to have positive effects at uor sessions to repaire/ modify or better refusing the Tanks. I hope I could do that as well as possible.



#13 gregga

gregga

    Brand New Member

  • Members
  • 9 posts

Posted 12 March 2013 - 03:01 PM

Following the line of PROINWV and Mr Shah, I suggest that you have a vessel design engineer physically inspect the tank and re-evaluate the rating of the vessel.  This is your starting point.  Have the vessel engineer then specify the % over pressure that would be allowed for relief calculations.  Depending on the design, you may be allowed anywhere from 0% overpressure to 10% overpressure in the relief calculation.

 

Go to a press / vac vent supplier and find the performance curves for your situation and design basis.  Assuming 0% overpressure is allowed, what pressue would you have to set the pressure side in order to relieve your calculated relief rate such that the pressure never exceeds the pressure rating.  Do the same thing on the vacuum side (using the in-flow vapor rate).  Once you have these parameters, you can talk to an instrument engineer to determine if there is suffient spread between the pressures to provide pad gas control (including some dead band)--you could  have a difficult time in this application