Is there any equation for calculating relieving temperature for wetted vessel like unwetted vessel for Fire Case?
Also in the case of other relieving scenarios? Any code or regulations?
Many Thanks.
Shahidul
Posted 17 February 2017 - 05:56 AM
Many Thanks.
Shahidul
Posted 17 February 2017 - 07:11 AM
Shahiidul,
If the liquid inside the vessel is a pure component, the relieving temperature would be liquid boiling point corresponding to the relieving pressure...
If the liquid is a multicomponent, the relieving temperature wouldn't be fixed and be progressively increased as the boiling point of the liquid is going to be increased due to light components reduction...
Posted 17 February 2017 - 09:25 AM
Shahiidul,
Hi Fallah,
Thanks for your reply.
Since we have to mention both relieving pressure and temperature as pre-requirement for sizing PSV, for multi-component system wouldn't relieving temperature have any significance or we have to mention the temperature that corresponds to highest boiling point temperature?
Best Regards,
Shahidul
Posted 18 February 2017 - 02:03 AM
Shahidul,
For two phase and multicomponent systems in fire case the relieving temperature varies from IBP to FBP and continues up to a temperature where vessel would failed.
In fact, because in most fire cases it's logically assumed the PSV cannot protect the vessel from failure, relieving temperature wouldn't be so significant in relevant PSV sizing and can be taken a value between IBP and FBP; but if you are insisting to calculate reaching an exact value you can use both IBP and FBP and select the one leading to higher relieving area as relieving temperature.
Posted 18 February 2017 - 02:55 AM
Thanks Fallah for your input.
Superheat Limit TemperatureStarted by Guest_phoenixmoca_* , 28 Sep 2022 |
Chiller Efficiency Dependence On Cooling Water TemperatureStarted by Guest_Neha Vensiyani_* , 29 Apr 2024 |
Caloric Temperature CalculationStarted by Guest_bckesim_* , 10 Apr 2024 |
Falling Film Reactor Design CalculationStarted by Guest_Emranm02_* , 07 Apr 2024 |
Rh CalculationStarted by Guest_bckesim_* , 03 Apr 2024 |