A few things are not clear in your PID. Firstly, the nitrogen line you mentioned (blue), has got a spectacle blind in the closed position. If this is the line you use for purging during low low pressure, it shouldn't be closed in normal operating condition.
The NRV direction more or less confirms the flow direction, so yes, the two opposite arrows on the nitrogen line, dont make sense.
I think we could give you a better response if you showed us which/where is the line used to release EO to atmosphere/scrubber in cases of PIT 180A/B high high pressure. It is definitely NOT the green lines, since they are PSV discharges, which should be working independent of the instruments.
The reason I ask this is because usually for pressure control of EO tanks/vessels, the configuration is such that the vessel has a small stretch of common piping which is used to pressurise with nitrogen or release pressure to scrubber with split control valves. So, that small common stretch sees bidirectional flow, depending on the pressure situation. I tried to visualise that happening here, but at the moment, I couldnt figure it out from this drawing.