Designing A Plate & Frame Heat Exchanger
Posted 02 July 2010 - 03:55 AM
I'm trying to understand the concept to design a plate and frame heat exchanger (PHE) in a palm oil refinery.
I have the following datas:
Inlet temperature of bleach palm oil (BPO) : 100oC
Outlet temperature of BPO : 170oC
Inlet temperature of RBDPO : 194oC
Outlet temperature of RBDPO : 123.5oC
Mass flow rate of BPO: 35,000 kg/h
Mass flow rate of RBDPO : 33,500 kg/h
Specific heat © for BPO : 2.468 kJ/kgK
Specific heat © for RBDPO: 2.559 kJ/kgK
Now, the way i understand is I need to calculate the heat load (Q) in the PHE using Q=mc(theta) and I've calculated that
and get 1,679.95 kW.
The next step is to use Q = UAT ====> (T refers to T lmtd)
I already have the Q and I can calculate T (lmtd).
I need the U value (overall heat transfer coefficient) in order to get A (area).
When I get A, I can determine how much plate I need for my PHE (assume I know the area of a single plate).
Now, I cannot proceed because with the above equation to get A because I don't have U.
U depends on A and A also depends on U.
Any ideas what I should do?
I thought of using the formula :
1/u = 1/hu + x/k + 1/hi + Rf (Rf = fouling factor) to get the U value but the problem is I can't find value of
hu (heat transfer coefficient of BPO) and hi (heat transfer coefficient of RBDPO)
Any body can response and provide me some idea to solve this, I really appreciate it very much...
Thanks and best regardz
Posted 02 July 2010 - 06:21 AM
Let you go to Cheresources.com ( button left hand side) , you will get access to a paper on preliminary design for plates heat exchanger .
Hope this helps you
Posted 02 July 2010 - 11:21 AM
I don't know why anyone would like to calculate the PHE area. PHE's are still specilaized items and there are very specific vendors such as Alfa-Laval, GEA who supply PHE's and have specialized design procedures for PHE's. If the idea is to procure a PHE then you only need to fill a process data sheet in which you provide the flow rates (hot/cold fluid), physical properties (density, viscosity of hot/cold fluid), overall heat duty, allowable pressure drops (cold/hot side).
If you actually want to size a PHE then there are some specialized texts which deal with PHE's. Some guidance is also given in GPSA engineering databook.
Hope this helps.
Posted 02 July 2010 - 11:46 AM
Use equivalent diameter(Deq) for Reynolds number calculation. Deq is 4 times the cross sectional area of the channel divided by the wetted perimeter of the channel.
Thank You
Mahesh
Posted 02 July 2010 - 02:25 PM
Posted 02 July 2010 - 02:28 PM
Yep, I agree with you that the vendors have that specialized procedure, however I hope it is not wrong for us to know and comprehend the way of calculating and going about the sizing of PHE.
However, I really appreciate you giving me some tips on the handbook. I'll try and search for it now.
Cheers mate...
Posted 02 July 2010 - 02:31 PM
Is this method that you suggested appropriate for plate heat exchanger? I'm sorry, I'm a little bit confuse...
Posted 03 July 2010 - 01:16 AM
Posted 03 July 2010 - 04:20 AM
As Ankur suggested you should ask vendor (alfa laval, Danfoss ,...) to support your query .
Danfoss is providing a calculator tool (DANFOSS CALCULATION HEAT EXCHANGER Tool) you can dowload from internet .
Hope this helps .
Posted 03 July 2010 - 01:14 PM
Danfoss is providing a calculator tool (DANFOSS CALCULATION HEAT EXCHANGER Tool) you can dowload from internet.
Hello Breizh
That was an interesting link. Does the Danfoss' software have any references/track record regarding the accuracy of results obtained by using this particular package?
Thanks,
#11
Posted 03 July 2010 - 08:49 PM
Sorry I cannot answer your question .
Posted 04 July 2010 - 11:36 PM
Alzack,
HTRI is the best software for Plate & Frame Exchanger Design.I have used it and results are pretty close to those of vendor data sheets. HTRI manual is also available that provides complete descripition of the design procedure.
#13
Posted 06 July 2010 - 02:58 AM
An other resource from APV .
http://www.apv.com/p..._08_2008_US.pdf
Hope this helps .
Posted 06 July 2010 - 03:23 AM
HTRI and AspenTech (Aspen Plate Exchanger) are the 2 main software providers for this type of application. You can contact them to have a quote.
Kind Regards
![]() Heat Loss Calculation From Cylindrical Tan;Started by Guest_rasprocess2026_* , Yesterday, 02:04 AM |