Sizing Aircooler
Started by leyva_luis, Aug 06 2010 03:49 PM
7 replies to this topic
Share this topic:
#1
Posted 06 August 2010 - 03:49 PM
Hi, I'm sizing aircooler. Propane at conditions 138°F and 208.6 psig is desuperheating and condensing.Propane rate is 9166 lb/h. Propane is saturated liquid(113°F) at outlet conditions. Propano is in tube side. Air inlet at conditions 77°F and 14.7 psia. Air outlet 105°F.
I selected tubes OD 1in, BWG16, 2 3/8triangular spacing, fin high 3/8in, fin width 0.035in, density 8fins/in, fin material aluminium. I assumed duct size lengh 24ft,width 12ft.
I did calculations with Donald Kern's book (process of heat transfer). But Overall Coeficient(desuperheating) calculated was 6 BTU/h.ft2.°F and Overall coeficient(condensing) calculated was 65 BTU/h.ft2.°F. #tubes/row =60tubes, #row=3. I considered 1 pass for side tubes, and 2 fans.
The values of overall coeficient are good?
How can I determine power of fans?
Thanks in advance
I selected tubes OD 1in, BWG16, 2 3/8triangular spacing, fin high 3/8in, fin width 0.035in, density 8fins/in, fin material aluminium. I assumed duct size lengh 24ft,width 12ft.
I did calculations with Donald Kern's book (process of heat transfer). But Overall Coeficient(desuperheating) calculated was 6 BTU/h.ft2.°F and Overall coeficient(condensing) calculated was 65 BTU/h.ft2.°F. #tubes/row =60tubes, #row=3. I considered 1 pass for side tubes, and 2 fans.
The values of overall coeficient are good?
How can I determine power of fans?
Thanks in advance
#2
Posted 06 August 2010 - 04:29 PM
The condensing coefficient seems to be a bit high but we don't know whether it is expressed on a bare tube surface area basis, or did you use extended (total) surface area? Attached are some guidelines from the GPSA Databook for your reference. The same resource gives the procedure for calculating fan power as well, and also to check if the thermal design has been done correctly.
Additionaly, there is a software from Hudson which you can use for cross-checking your results. It is not meant to be a final design tool but it can certainly tell you whether you are in the same ball park.
http://www.hudsonpro.../ACHE2Setup.exe
http://www.hudsonpro...eV5.7 setup.exe
Additionaly, there is a software from Hudson which you can use for cross-checking your results. It is not meant to be a final design tool but it can certainly tell you whether you are in the same ball park.
http://www.hudsonpro.../ACHE2Setup.exe
http://www.hudsonpro...eV5.7 setup.exe
Attached Files
#3
Posted 06 August 2010 - 05:58 PM
Zauberberg,
I attached the spreadsheet for aircooler.
Checking and comments.
Thanks in advance
I attached the spreadsheet for aircooler.
Checking and comments.
Thanks in advance
Attached Files
#4
Posted 07 August 2010 - 12:05 PM
You have calculated 8.8 BTU/hr.ft2.°F as the air film coefficient, and 240 BTU/hr.ft2.°F as the Propane film coefficient, and then you come up with 65 BTU/hr.ft2.°F being the overall heat transfer coefficient which is not possible.
The way it should be calculated (without taking into account fouling resistance - which should be accounted for, by the way - otherwise you will end up with an undersized air cooler), is:
1/U = 1/ho + 1/hi = 0.1176, therefore U = 8.5 BTU/hr.ft2.°F
If you add the fouling contingency factor, you'll probably end up with a U-value closer to 5.5 - 6.0 BTU/hr.ft2.°F which is a guideline figure from the GPSA Databook table attached in my previous post.
Best regards,
The way it should be calculated (without taking into account fouling resistance - which should be accounted for, by the way - otherwise you will end up with an undersized air cooler), is:
1/U = 1/ho + 1/hi = 0.1176, therefore U = 8.5 BTU/hr.ft2.°F
If you add the fouling contingency factor, you'll probably end up with a U-value closer to 5.5 - 6.0 BTU/hr.ft2.°F which is a guideline figure from the GPSA Databook table attached in my previous post.
Best regards,
#5
Posted 08 August 2010 - 12:03 AM
levya_luis,
One downloadable software for air cooled heat exchangers is available at:
http://www.hudsonpro...m/download.html
Another online calculator for ACHE's by GEA-Rainey is available at:
http://www.gearainey...Calculator.html
The Hudson Products Corporation software also provides "overall heat transfer coefficient" based on a selction of applications.
Hope this helps.
Regards,
Ankur.
One downloadable software for air cooled heat exchangers is available at:
http://www.hudsonpro...m/download.html
Another online calculator for ACHE's by GEA-Rainey is available at:
http://www.gearainey...Calculator.html
The Hudson Products Corporation software also provides "overall heat transfer coefficient" based on a selction of applications.
Hope this helps.
Regards,
Ankur.
#6
Posted 03 October 2010 - 08:17 AM
Dear Zauberberg:
Can you please provide the spreadsheet in .xls format. I have Excel 2003 loaded, and this updated type (i.e. xslx) does not open in my 2003 version.
Thanks in advance
Unmesh Biswas
Can you please provide the spreadsheet in .xls format. I have Excel 2003 loaded, and this updated type (i.e. xslx) does not open in my 2003 version.
Thanks in advance
Unmesh Biswas
#7
Posted 03 October 2010 - 08:47 AM
There is a Microsoft Office Compatibility Pack for Word, Excel, and PowerPoint File Formats which allows you to open MS Office 2007 files through previous MS Office versions, available for free download from:
http://www.microsoft...&displaylang=en
Download, install, and run.
http://www.microsoft...&displaylang=en
Download, install, and run.
#8
Posted 04 October 2010 - 03:50 PM
I am supprised at the fin configeration used. Normal is 5/8 inch high fins and 10 fins/inch. For fan HP, you can also contact Moore fans and they have free software to calculate the HP.
Similar Topics
![]() Liquid Liquid Separator SizingStarted by Guest_Kentucky08_* , 03 Apr 2025 |
|
![]() |
||
Critical Pressure For Choke Valve SizingStarted by Guest_Sherif Morsi_* , 07 Nov 2017 |
|
![]() |
||
Alkaline Electrolytic Cell/stack Sizing/design For H2 ProductionStarted by Guest_BRS09_* , 13 Mar 2025 |
|
![]() |
||
Batch Adsorption: H/d Ratio For Vessel SizingStarted by Guest_Victor_process_Engineer_* , 28 Feb 2025 |
|
![]() |
||
![]() Separator Sizing Step By Step ProcedureStarted by Guest_krishnamurthy_* , 06 Apr 2023 |
|
![]() |