Valve Type For Min Flow In Fire Water Pumps
Posted 18 August 2010 - 02:55 AM
Posted 18 August 2010 - 07:22 AM
Posted 18 August 2010 - 01:23 PM
Posted 21 August 2010 - 06:13 AM
Posted 21 August 2010 - 07:21 AM
Can you upload the P&ID?
Posted 22 August 2010 - 04:11 AM
The attached document may help for a better understanding.
Posted 22 August 2010 - 04:34 AM
Posted 22 August 2010 - 05:25 AM
I know the control philosophy of the system exactly, but want to know about applying a PCV instead of a FV/PV.
Posted 22 August 2010 - 11:38 AM
1. Let's say you open a bleeder somewhere in the fire water system;
2. The ring main pressure starts to drop slowly;
3. Based on the pressure switch settings, the Jockey pump kicks-in and tries to raise the system pressure;
4. Once when the system pressure reaches the PCV set point (which is above the Jockey pump kick-out pressure set point), the valve opens and starts recycling water back to the tank. I believe the PCV is required since there is a minimum run time for the pump, and the pump cannot be simply shut down once when the ring main pressure reaches or exceeds the set point.
I'm looking into our fire water system P&ID and there are no PC valves in the Main Fire Water pump discharge line - just a relief valve. Note on the P&ID says: "The jockey pump controller shall automatically start and stop the pump to maintain the system standby pressure. Kick-in pressure: 9.7barg, kick-out pressure: 10.2barg".
I hope Guido is reading this thread and hopefully he can clarify the subject completely.
#10
Posted 22 August 2010 - 12:18 PM
- System overpressure protection
- Pump minimum flow provision
But, perhaps I am wrong so let's hope an expert will reply to this thread.
#11
Posted 22 August 2010 - 12:25 PM
#12
Posted 23 August 2010 - 02:10 AM
In our system, contrary to your system, the jockey pump is continiously running and obviously needs to be furnished by a minimum flow line (as a consequence of running normally with no flow in order to maintain the pressure).
#13
Posted 23 August 2010 - 01:37 PM
With a PCV, things are somewhat easier in my opinion: as the pressure switch kicks-in the Jockey pump, it starts to pump water into the system, and as the ring main pressure increases, the pump flow decreases due to higher differential head requirements (the pump moves left on the operating curve). At a certain point, which should be the differential head corresponding to the minimum flow, the PCV opens and starts to recycle water back to the tank. That way the pump serves its purpose - maintaining system pressure - while at the same time there is provision for minimum flow.
#14
Posted 24 August 2010 - 01:58 AM
Thank you for feedback on the subject. I was trying to depict this particular arrangement assuming a flow control valve in the recycle line, and I believe it would be quite difficult to design such a system when knowing that the Jockey pump has to run in between the kick-in/kick-out pressure switch settings, and maintain the minimum flow at the same time. Since there is no control valve in the main discharge line (or any kind of variable resistance device), I wonder what would force the Jockey pump - apart from the ring main pressure itself - to push water into the system and not through the recycle line.
Agreed with your above nice explanations!
#15
Posted 24 August 2010 - 06:16 AM
Continuous operation of Jockey pump indicates some significant leakages in your system, in my opinion - unless you use fire water intentionally for some other purpose. So perhaps a quick field investigation can reveal what is all about.
This was very interesting topic, with a few good learning points. Thanks for posting.
Posted 24 August 2010 - 06:50 AM
Good point!
The pipe material of fire water network i attached (as PID) to one of my previous posts,is GRP that as per your above logical statement,because of almost poor mechanical strength tends to be subject to leakage especially on fitting connections.
#17
Posted 25 August 2010 - 03:54 PM
Flow control is more precise than pressure control and this is usually applied. But is it more reliable? Flow control requires electronic flow transmitter interlocked with the control valve (through DCS in the majority of cases). I think mechanical interlock is not feasible in such a case; or it would be too complex (as a system), if existed.
Nevertheless mechanical return flow valves (type Yarway or similar) can be found in some critical applications (e.g. liq NH3, boiler feed water). These valves need no electronic parts for action and are usually supplied together with the pump. These are more reliable in comparison to valves controlled electronically, for they can operate even when electronics fail, which is possible during fire.
I assume that these mechanical valves are pressure controlled and they are used on firefighting pumps due to their higher reliability. I do not know whether it is mandatory by NFPA; it may be so, since relevant codes require pump operation at any case, even under power failure (so min flow shall be operable even under electronic failure).
Selection Type Of Heater For Refrigerated PropaneStarted by Guest_livetolove003_* , 07 May 2025 |