Dear All, with due respect , I would like to point out few important points on the configuration specified in the P&ID,
If not wrong the FE in the suction side is being used for Shut Down service. My gut feeling says that this is a wrong location for sensing a low low signal. Ideally it should be downstream of strainer shown. Also the type of FE used is wrong, the orifice will create further pressure drop and Net NPSHa will reduce down.
Basically it is not recommended to put any kind of restriction in suction line, but what i understand from configuration is that " The FE used in suction line is to protect pump in case of low low flow if the pump discharge fails to open". Downstream FE after pump will protect the pump in case of low flow upto the minimum flow of pump as specified by pump vendor in case of discharge valve closure. But what about if pump discharge valve struck at 5% open condition ( actual case of MOV in pump discharge).
Various pump manufacture recommends that low energy pumps upto 160 kW can run against closed discharge upto 5 seconds, and high energy pumps upto 2 sec.
The crux is that, the FE ( orifice type) wont be able to protect the pump, instead of that we have to provide certain other means like
1. Low flow switch ( Thermal dispersion type , the same i have used for one of our project in Oman)
2. Motor trip via measuring load current
3. PT with PAHH trip
awaiting for any clarification or kind suggestions.
best regards
Dev