I am working on a project of storage tank installation for a flammable liquid. It is an atmospheric storage tank designed for the pressure of +56mbarg and vacuum of –6mbarg. Stored material is flammable and therefore, tank is provided with N2 blanket line at 20mbarg. The tank will be filled and emptied using a single pump.
Please see the attaché P&ID for the tank. Sorry, I could not format it properly which would cause some problem in viewing it. Please not that pump discharge line to tank is 40mm and not 25mm as shown in the P&ID.
There are three pressure protection devices/provisions. (1) 6” Liquid Overflow line – This line is installed with pressure relief valve [PDPV 2355/2] which is set at a pressure of 40mbarg (2) 6” pressure vacuum vent valve [PDPV 2355] which is set at a pressure of +25mbarg and vacuum of –2.5mbarg (3) 24” Emergency pressure relief man way [PDPV 2355/1] is set at a pressure of 45mbarg.
My queries are as below:
Personally I think, the set pressure [40mbarg] of 6” relief valve [PDPV 2355/2] at liquid overflow line is wrong as liquid overflow line would be my primary protection device in the event of tank overfill and therefore, PDPV 2355/2 should be triggered first. Set pressure of PDPV 2355/2 should be greater than the N2 blanket line [20mbarg] and less than set pressure of 6” pressure vacuum vent valve [25mbarg], let’s say 22mbarg. However, if I do so, during tank filling, PDPV 2355/2 will be activated first and NOT pressure vacuum vent valve [PDPV 2355].
How do we decide/calculate the set pressure for PDPV 2355/2?
If the set pressure of PDPV 2355/2 is let’s say 22mbarg and it activates during tank filling, will it create any problem? If it will not create problem, what will be the use of having pressure vacuum vent valve whose set pressure is 25mbarg apart from vacuum protection?
Client wish to offload a tanker at 20m3/hr and empty a tank to reactor at 10m3/hr. I see a problem in tanker offloading due to high velocity. As the pump discharge line to a tank is 40 mm, the line velocity is 4.82m/sec [somehow [client is OK up to a line velocity of 5m/sec] and Raynolds Number is about 220,000 which is very high. Do you think, such a high velocity/turbulent flow will create any problem in terms of static discharge? I can see another problem of higher pumping cost due to higher pressure drop at such a high velocity and it’s very difficult to convince the client to increase the pipe size as they have ordered pipes/fittings etc.
Do you see any other problem in the attached P&ID?
Your help would be highly appreciated.
Regards