In all the projects,I find that consultant has specified Cooling water return temperature to be 45 degc,not more or less than that.
What is the reason behind it?
|

Cooling Water Return Temperature
Started by A mukherjee, Nov 18 2010 02:29 PM
2 replies to this topic
Share this topic:
#1
Posted 18 November 2010 - 02:29 PM
#2
Posted 19 November 2010 - 06:04 AM
45 degC is being considered - based on field experience - as the upper practical limit for cooling water return temperature. Reason: deposition of Carbonate salts at higher temperatures, resulting in accelerated fouling and plugging of heat exchanger.
Certainly you may choose lower return temperature, but this would lead to higher CW flow requirements = higher size/cost of the cooling water system, and in some cases bigger exchangers as well, capable to handle larger coolant flows.
Certainly you may choose lower return temperature, but this would lead to higher CW flow requirements = higher size/cost of the cooling water system, and in some cases bigger exchangers as well, capable to handle larger coolant flows.
#3
Posted 21 November 2010 - 02:02 PM
Thnxx Zauberberg for the reply.
Generally for most of the projects I 've found CWS temp to be 33 degc & CWR to be 45 degc,specified in the contract document.
But in reality(eg.in refrigeration unit,compressor intercoolers),Cooling water temp rise is not more than 4 degc.
Is there any particular reason to fix the Cooling water temperature rise arnd 4 degc?
Generally for most of the projects I 've found CWS temp to be 33 degc & CWR to be 45 degc,specified in the contract document.
But in reality(eg.in refrigeration unit,compressor intercoolers),Cooling water temp rise is not more than 4 degc.
Is there any particular reason to fix the Cooling water temperature rise arnd 4 degc?
Similar Topics
Water Hammer Study: Hysys Dynamics Vs PipenetStarted by Guest_powerox29_* , 07 Apr 2025 |
|
![]() |
||
![]() Steam Carrying Liquid From The Sour Water Stripping TowerStarted by Guest_kaidlut_* , 12 Sep 2024 |
|
![]() |
||
Water TreatmentStarted by Guest_not_mikhail_* , 01 Apr 2025 |
|
![]() |
||
Cross Over Temperature In Countercurrent Heat ExchangerStarted by Guest_panoska_* , 18 Feb 2025 |
|
![]() |
||
![]() Transfer Water By Gravity - Maximum Velocity CriteriaStarted by Guest_56200358_* , 05 Mar 2025 |
|
![]() |