I am going through my notes and looking to summarize the differences in Natural versus Forced draft operation in water bath heater operating.
The differences are:
1. In size of Fire tube: Natural draft operation leads larger diameter size of the fire tube and this makes heater shell larger.
2. Flux Rate: Natural draft operation allows to design for 10,000btu/hr-ft2 flux rate on the fire tube but with forced draft you can use higher flux rate, such as 20,000btu/hr-ft2. So this makes fire tube smaller on forced draft operation
3. Natural draft operation cannot have flexible turndown but forced draft burners can have 100:1 turndown capacity
4. Natural draft operation has higher emission due to higher excess air
5. Forced draft needs combustion air fan and purges flue gases easily from the tube but natural draft does not require any fan. It uses large amount of oxygen and for purging they need a purge fan for the fire tube to purge
6. Natural draft operation needs less capital. But forced draft has high capital cost due to the electric demand. I cannot elaborate on operating cost because it is really different for each company operation.(?)
7. Natural draft operation start up is difficult then forced draft.
Anything I missed?
Please let me know your thoughts. Thank you.