Dear Process Expert
A process engineer claimed that Spectacle blind should be considered as "Block Outlet" Source for PSV.
I am sure it is not ture as very obvious issue.
But I share this point for more clarification.
Please put your points based on some facts and practice.
GB
Spectacle Blind And Blocked Outlet For Relief
Started by Ghasem.Bashiri, May 11 2011 11:05 AM
Posted 11 May 2011 - 11:05 AM
Posted 12 May 2011 - 12:14 AM
Dear Ghasem,
If he/she means the spectacle blind in upstream/downstream of the PSV,he/she is right and for this reason,during maintenance in oppose to other nozzles of a vessel,PSV nozzle isolated with the vessel by removing a preinstalled spool piece of pipe and subsequent blinding.Other nozzles would be isolated by spectacle blinds.
Fallah
Fallah
Posted 12 May 2011 - 03:50 AM
Ghasem,
Fallah is right, you should certainly use a removable spool and not a spectacle blind to isolate a vessel from a PSV.
For other spectacle blinds, it is difficult to imagine a case where there is a spectacle blind without a manual block valve in the same line. Therefore, the manual block valve can be closed and so cause blocked outlet, and the blind in the same line does not give rise to an additional relief case or a different relief case from that of the block valve.
Paul
Paul
Posted 12 May 2011 - 06:38 AM
No, Mis Understanding!
Assume a system without manual valve. Is it required and possible to consider Spectacle blind (Spade/Spacer) as source of overpressure (block outlet).
I think for such blockage we should shut down the system and change position of Spectacle or Spade/Spacer.
Or alternatively someone may forget to change position of Spectacle blind during startup from close to open and then system can be block!!!
Is it required to consider this issue as source of over pressure and block outlet.
GB
GB
Posted 12 May 2011 - 08:26 AM
Ghasem,
To avoid any misunderstanding, please SEND US A DIAGRAM, showing exactly where this blind is and which equipment is in danger of overpressure.
Before you send a diagram, please note that the PID which you have just sent through on the Relief Devices Forum, which seems to be about the same set of problems which you have asked about, does NOT show where this blind is located.
This is quite correct, that is the time when you will get a mal-operation. So, do not use a spectacle blind, use a removable spool, which cannot cause a blocked system.
This series of posts from you, since February, is becoming a detailed PID review, free of charge, while you are being paid to resolve these problems. I don't think that is an appropriate use of this forum.
Paul
Paul
Posted 14 May 2011 - 04:05 AM
No, Mis Understanding!Assume a system without manual valve. Is it required and possible to consider Spectacle blind GB
Mentioned misunderstanding is the result of presenting your query without adequate information/explanation,supporting sketch,.....
Considering the above, you shouldn't expect the forum members to know what exactly is in your mind about the query!
Parallel Control Valves Downstream Relief ScenarioStarted by Guest_pklavinsJ_* , 18 Jun 2025 |
Blocked Outlet For Continous SourceStarted by Guest_56200358_* , 03 Feb 2025 |
![]() Tube Rupture ReliefStarted by Guest_felderosfelder101021_* , 16 Jan 2025 |