why even number of tube passes(except 1-pass) prefer in shell and tube heat exchanger? can we prefer odd number of passes?
|

Number Of Tube Passes In Shell And Tube Heat Exchangers
Started by suryatej001, Oct 27 2011 10:29 AM
4 replies to this topic
Share this topic:
#1
Posted 27 October 2011 - 10:29 AM
#2
Posted 28 October 2011 - 03:17 AM
1. Theoretically, odd passes can be used
2. Practically, from construction, installation and maintenance view point, even number is prefereable
3. Take note that the inlet and outlet for odd passes is on the opposite end.
2. Practically, from construction, installation and maintenance view point, even number is prefereable
3. Take note that the inlet and outlet for odd passes is on the opposite end.
#3
Posted 28 October 2011 - 10:59 AM
thanks S.AHMAD sir
Edited by suryatej001, 28 October 2011 - 11:00 AM.
#4
Posted 28 October 2011 - 11:14 AM
Hello,
Those are good comments by S. Amhad.
1. One tube pass floating heat or pull thru heat exchangers are rare and tend to leak at the floating head end if packing is used. I have never seen three or more odd number of tube passes in this type of heat exchanger.
2. Odd number of tube passes is out of the question for u-tube heat exchangers.
3. There are many fixed tube sheet heat exchangers with one tube pass. In the years that I have designed and rated heat exchangers I have seen only several three tube pass units.
Those are good comments by S. Amhad.
1. One tube pass floating heat or pull thru heat exchangers are rare and tend to leak at the floating head end if packing is used. I have never seen three or more odd number of tube passes in this type of heat exchanger.
2. Odd number of tube passes is out of the question for u-tube heat exchangers.
3. There are many fixed tube sheet heat exchangers with one tube pass. In the years that I have designed and rated heat exchangers I have seen only several three tube pass units.
#5
Posted 28 October 2011 - 01:27 PM
Thank you very much for your reply.
Similar Topics
Steam Pressure In Heat ExchangerStarted by Guest_mvanrijnbach_* , 15 Apr 2025 |
|
![]() |
||
![]() Rotated Triangular Tube Layout Vs Triangular Tube LayoutStarted by Guest_Heat Transfer Novice_* , 28 Sep 2024 |
|
![]() |
||
Heat Exchanger Steam FlowStarted by Guest_aliebrahem17_* , 25 Nov 2024 |
|
![]() |
||
![]() Supercritical Fluid Flowrate - He Tube RuptureStarted by Guest_flarewolf_* , 07 Apr 2025 |
|
![]() |
||
Discussion - Predict Storage Tank Heat Transfer Precisely By Jimmy D KStarted by Guest_raj shekhar_* , 25 Mar 2025 |
|
![]() |