Good Evening,
I am currently desiging a heat exchanger to heat Air from 10 oC to 110oC and cool flue gas from 1259.4 oC to 725 oC.
As both fluids are gases, i would like to know if it is advicable to use a shell and tube heat exchanger?
I read online that the convertional gas-to-gas heat exchanger is vertical shell and tube heat exchanger
Thank You Very Much
Kind Regards
Paul
|

Heat Exchanger Design
Started by djdemzy, Feb 15 2012 01:25 PM
3 replies to this topic
Share this topic:
#1
Posted 15 February 2012 - 01:25 PM
#2
Posted 15 February 2012 - 04:11 PM
Hello,
This appears to be an air preheater of some kind. It would not be a conventional shell-and-tube. Because of the low heat transfer coefficients on both sides, there needs to be some kind of extended surface.
This appears to be an air preheater of some kind. It would not be a conventional shell-and-tube. Because of the low heat transfer coefficients on both sides, there needs to be some kind of extended surface.
#3
Posted 16 February 2012 - 02:25 AM
#4
Posted 17 February 2012 - 01:13 AM
As srfish mentioned your application is air preheater.One of good example is heat recovery excahger in Power industry, when outlet flue gas from boiler used for preheating of air.Take a look
in following link for some kind of this type of exchangers:
http://www.airprehea...?cat=1&subcat=9
in following link for some kind of this type of exchangers:
http://www.airprehea...?cat=1&subcat=9
Similar Topics
Refinery Lpg Deethanizer Column DesignStarted by Guest_Ilyes_* , 15 Feb 2025 |
|
![]() |
||
Steam Pressure In Heat ExchangerStarted by Guest_mvanrijnbach_* , 15 Apr 2025 |
|
![]() |
||
Heat Exchanger Steam FlowStarted by Guest_aliebrahem17_* , 25 Nov 2024 |
|
![]() |
||
Discussion - Predict Storage Tank Heat Transfer Precisely By Jimmy D KStarted by Guest_raj shekhar_* , 25 Mar 2025 |
|
![]() |
||
Alkaline Electrolytic Cell/stack Sizing/design For H2 ProductionStarted by Guest_BRS09_* , 13 Mar 2025 |
|
![]() |