This may well be covered elsewhere in the forums but I haven't been able to find it so feel free to point me in the correct direction if I've missed it.
I wondering how a control valve can increase the allowable pressure drop before choked conditions are met?
I've been calculating the maximum gas flow through a control valve in order to check a relief valve sizing scenario. To do this I've been using the ANSI/ISA Flow Equations for Sizing Control Valves.
In these equations x=deltaP/P1=1-(P2/P1) and x<=Fk*Xt
Typical values of Xt that I have found range from c.a. 0.3 - 0.9
If we assume we are looking at air so the heat capacity ratio,k = 1.4 then Fk=1 and x is totally dependent on Xt. If Xt =0.9 then x=0.9 and flow through the valve becomes choked at P2/P1=0.1
If I assume the gas in question is ideal I can apply to following condition at choked flow P1/P2=[ ( k + 1 ) / 2 ] k / ( k - 1 ). This suggests that P2/P1~0.5 at choked conditions.
Can anyone explain how a control valve can increase the allowable pressure drop before choked conditions are met?
Thanks
|

Gas Phase Control Valve Pressure Drop Ratio Factor, Xt
Started by antator, Apr 02 2012 01:09 PM
control valves critcal flow xt control valve
2 replies to this topic
Share this topic:
#1
Posted 02 April 2012 - 01:09 PM
#2
Posted 03 April 2012 - 02:12 PM
Antator,
Refer the attachment regarding the sizing of valves by Parker. It may provide you the answer you are looking for.
Regards,
Ankur
Refer the attachment regarding the sizing of valves by Parker. It may provide you the answer you are looking for.
Regards,
Ankur
Attached Files
#3
Posted 04 April 2012 - 04:28 PM
Thanks for the reply.
I still find it curious that Xt values up to c.a. 0.9 are possible given that through an orifice I would normally expect choked flow to occur at approximately 0.5 asssuming ideal behaviour. I guess I will have to accept this for the time being.
I still find it curious that Xt values up to c.a. 0.9 are possible given that through an orifice I would normally expect choked flow to occur at approximately 0.5 asssuming ideal behaviour. I guess I will have to accept this for the time being.
Similar Topics
![]() Relief Path To Be Considered For Inlet Pressure Drop CalculationStarted by Guest_Ascanio E._* , 09 Jul 2025 |
|
![]() |
||
![]() Valve Cv InputsStarted by Guest_QuantumEng_* , 01 Apr 2024 |
|
![]() |
||
![]() Negative Pressure Discharge / Negative At High PointStarted by Guest_felderosfelder101021_* , 05 Jul 2025 |
|
![]() |
||
![]() Rupture Disc Failure Well Below Max PressureStarted by Guest_vaibhav02_* , 02 Jul 2025 |
|
![]() |
||
![]() Distillation Column Top PressureStarted by Guest_halkeshhulk_* , 27 Jun 2025 |
|
![]() |