Dear all,
I have heat exchanger with water and HC streams If I will change water outlet temperature - as result HC outlet temperature will change as well. Flow is const. Does it changes are depend with heat trans. area of exchanger? If no what will be change? How I can see it in Hysys? Regards.
|

1 reply to this topic
Share this topic:
#1
Posted 10 April 2012 - 06:36 AM
#2
Posted 10 April 2012 - 07:51 AM
HI Dear.
you know that heat transfer in exchanger calculate as:
Q=F*U*A*LMTD
F= correction factor ,
U=Overall Heat transfer coef.
A=Heat transfer area,
LMTD=Log mean temp difference.
so you can change any of this parameter to changing heat transfer in H.X. now in Hysys simulation, you can change area by changing number of Tubes or F factor by changing exchangers configuration. I think in your simulation file, the Value of LMTD changed
you know that heat transfer in exchanger calculate as:
Q=F*U*A*LMTD
F= correction factor ,
U=Overall Heat transfer coef.
A=Heat transfer area,
LMTD=Log mean temp difference.
so you can change any of this parameter to changing heat transfer in H.X. now in Hysys simulation, you can change area by changing number of Tubes or F factor by changing exchangers configuration. I think in your simulation file, the Value of LMTD changed
Similar Topics
Aspen Hysys Simulation Of Acid Gas Removal UnitStarted by Guest_R.t_* , 22 May 2025 |
|
![]() |
||
Steam Pressure In Heat ExchangerStarted by Guest_mvanrijnbach_* , 15 Apr 2025 |
|
![]() |
||
![]() Hysys Expander/compressor Input Using Dimensionless CurveStarted by Guest_Alfreedo_* , 21 Apr 2025 |
|
![]() |
||
Water Hammer Study: Hysys Dynamics Vs PipenetStarted by Guest_powerox29_* , 07 Apr 2025 |
|
![]() |
||
Heat Exchanger Steam FlowStarted by Guest_aliebrahem17_* , 25 Nov 2024 |
|
![]() |