Interpretation by gegio1960 is judged reasonable to me; besides debutanizer PSV can be directed to flare header when its size gets high enough. Clarification is needed on the point raised by fallah in the preceding post, but let us presently assume no isolation between debutaniser and reflux drum (being "in open communication") during the scenaria involving the pair of PSVs.
Under these conditions, distinct functions of the PSVs are (α) discharge only from reflux drum PSV, (β) discharge from both PSVs simultaneously. Drum's PSV is set at 195 psig, debutaniser's at 200 psig. Can a set pressure difference of only 5 psi (2.5% of gauge set pressure) be enough for events (α) and (β) to be timely dinstict, or only (β) will occur in practice? Advice on the point is welcomed. Difference between set pressures may need increase, depending on the answer.
An example of similar case concerns two PSVs on a (ASME) boiler steam drum. First PSV is set at drum gauge design pressure, second at 3% higher (rounded to nearest 5 psi), according to instructions found (~1985). In an actual boiler (ordered in 2000) set pressures are 54.00 and 55.00 kgf/cm2 g (difference=1.8%), while allowable overpressure is only 3% for both PSVs. This may indicate that set pressure difference of 2.5% can be adequate, even though overpressure is not well understood (full relief of PSV1 at 54*1.03=55.62 kgf/cm2 g, while PSV2 starts opening at 55.00 kgf/cm2 g). But it concerns ASME boilers, not process equipment.
At any case clarifying allowable overpressure by Anup87, from the data sheets of two PSVs (set at 195 and 200 psig), would be useful.
Edited by kkala, 16 September 2012 - 01:49 PM.