Hello everybody..
I'm now working in optimizing biomass power plant design.
I want to use maximum amount of heat available from the flue gas.
The sulphur content of the biomass is 0.05%, and the system will be using dry sorbent injection for flue gas desulphurization.
From the formula I found on this forum, the acid dew point will be approximately be 70C.
The question is, what will the minimum allowable stack temperature be?
because I read in some rules-of-thumb article, that power plant with natural gas as its fuel will generally produce flue gas with acid dew point of 55C, but its minimum stack temperature should be >100C
Now I'm wondering, what exactly is the correlation between dew point and minimum stack gas temp?
Thank you,
Relation Between Dew Point And Stack Temperature
Started by Pheasant, Oct 16 2012 03:52 AM
dew point stack temperature
Posted 16 October 2012 - 03:52 AM
Posted 16 October 2012 - 10:48 PM
May be this link helps
http://www.jehar.com/dewpnt.htm
The stack temperature should be more than 30~50 deg C than the dew point.
Posted 17 October 2012 - 12:26 AM
Dew point, especially for flue gases with acid gases, is an indication on how low (temperature) you can operate without the possibility of corrosion (due to condensed acid gas) by placing some margin above the dew point temperature.
Posted 17 October 2012 - 05:46 AM
Based on the pressure fraction, you know the volume fraction.
Based on the concentration of condensing gases ,you can get the Dewpoint.
Lower the concentration , the dew point will be lower -which means you can extract more( heat )energy by keeping the exit gas temp at +20 Deg above condensing-dew point temp.of gases.
Numerical calc., charts , Mole frn/Partial pr vs Dew point are available.
Posted 17 October 2012 - 06:25 AM
YOU MAY REFER DEWPOINT CALCULATORS-Perma pure llc site for further info.
![]() Pipe Fluid Temperature Increase Due To Solar LoadingStarted by Guest_HeemeshJ126_* , 06 Apr 2016 |