I hope you are having good time.
I have an urgent request about finding Nitrogen gas volume.
Given Data: Tank Volume = 760 cu.m
This is Propane storage tank and we want to pressurize this tank upto 11.3 barg.
There are two cases:
Case 1: Pressurizing from 0(Zero)barg to 11.3 barg
Case 2: Pressurizing from 0(Zero)barg to 7 barg and then 7 barg to 11.3barg
I want to find the Nitrogen volume required which we have to buy. I think we need an additional volume for purging and inerting before pressurizing with nitrogen.
I am looking forward to your experiences and help.
Thank you so much in advance.
Best Regards
S. Sajid
PS: I calculated as follows:
Volume 760 cu.m
26839.4 cu.ft
Pressure 11.3 barg
12.3 bara
178.3992 psia
z 0.999
R 10.73 (ft^3*psia)/(lbmol*R) or 8.314 JK-1Mol-1
T 30 C
851.4 R
n= (P*V)/(z*R*T) 524.5858088 lbmol
Now at standard conditions the ideal gas law applies
T 527.67 R
P 14.7 psia
n 524.5858088 lbmol
V= n*R*T/P 202051.1 cu.ft
5721.39 cu.m
Pressurizing Propane Storage Tank With Nitrogen Gas
Started by ssengr62, Nov 09 2012 02:15 AM
Posted 09 November 2012 - 02:15 AM
Posted 11 November 2012 - 05:28 AM
hi
i am sure you are not looking at decimal values or accuracy level to last m3 of gas; then the simple way to estimate is:
tank vol =760 m3
n2 in the tank (when pressurized to 11.3 barg, ie at 12.3 bara;) 760 x 12 = 9600 sm3 (ignoring temp effect, compressibility etc and rounding off to 800 m3 volume for tank)
n2 in the tank at 7 barg (ie 8 bara) = 6400 sm3; and n2 required from 7 barg to 11.3 barg = 3200 sm3;
now coming to drying and purging; it depends on your use of N2 intially; i would look at 5 cycles; pressurize 0 barg to 2 barg and depressurize to flare press ~0.2, 0.3 barg and repeat again; if you ensure all vents/drains are properly blown with n2 and no pockets are present, you should get at the end of the 5th cycle a good lab report for o2 and moisture. the gas required for this would be 12000 sm3; if you have good operation team you can do it even with 0~1.2 barg to 0.2 barg cycle; which would be ~7000 sm3 only.
if you are pressurising to 7 barg and 11.3 barg for leak test then you can use that N2 fto cut the cycle to 3 times initially; finally, if you are using your propane storage as N2 hold for drying other parts of the plant, then i would advise you ensure that your propane tank is dried first before building the stock
tank vol =760 m3
Posted 11 November 2012 - 11:06 PM
Foam System Criteria For Hc Condensate Storage TanksStarted by Guest_Haideri_* , 28 Oct 2025 |
Atmospheric Tank Vent SizingStarted by Guest_kmic_* , 30 Sep 2025 |
Storage Tank Relief LoadStarted by Guest_hum464_* , 10 Sep 2025 |
Refrigerated Storage Tank Vaccum Breaker CapacityStarted by Guest_Lyne_* , 13 Sep 2025 |
Is Emergency Venting Required For Polyethylene Storage Tank In Fire ScStarted by Guest_chem55_* , 01 Aug 2025 |