Following notes may be useful
1. Met local deaerators operate at ~ 0.10 barg, 102 oC (design pressure= 2 barg). Boiler feed water (BFW) pumps are located underneath, so that difference NPSHa - NPSHr = 3 m. Oxygen scavenger is injected just downstream of deaerator surge drum.
2. By increasing deaerator pressure, NPSHa remains same (as clarified in previous posts). Suction head of BFW pump (thus total head) also increases correspondingly, which may not be significant for a boiler producing e.g. steam of 40 barg.
3. Main advantage of introducing waste steam into deaerator is fuel saving, since BFW is heated to some extent there, to rest extent in the economizer (and BFW heater, if any). I cannot say that Q (kW) offered by extra steam into deaerator results in savings of Q (kW) of fuel, based on NHV. Probably fuel saving is less, but there is. That is why flash steam from continuous blow down is directed into deaerators in a local refinery.
4. A supplementary advantage of hotter BFW is less risk of acidic corrosion from flue gases at economizer tubes (to get their temperature higher than acid dew point of flue gases). If there is a steam BFW heater for this purpose, BFW out will get hotter.
I vaguely remember a case where BFW heater could be eliminated by increasing deaerator pressure (1999).
5. Maximum temperature of hot water leaving economizer should be at least 25 oC below the saturation temperature at the steam drum, to avoid any vaporization in the economizer tubes, according to local practices (point mentioned in post no 10 by KLP).