Note/ experience: In boiler duty spec we have required such "continuous blow down drum" with flash steam directed to deaerator.
Flash drum has to be protected against overpressure even at max input flow. More flash steam will be produced at max input flow and PSV should have adequate capacity for that.
I think max flow rate through continuous blow down valve should be considered for PSV sizing. Existing PSV has to be checked for this case.
Well, all flash steam has to pass from PSV in case of blocked steam outlet. Ingoing boiler water has temperature about 292 oC. You do not want a vapor pressure higher than 95 psig in the flash drum, corresponding to ~168 oC. Flash steam through PSV will provide the necessary cooling (if outlet gets blocked).
Blocked steam outlet is assumed as credible contingency in this case, with water content of the drum being under level control and reacting relatively slow. I think it not safe to assume that the level control valve will prevent overpressure.