Cooling water circuits can be operated as described in post #4 by adjusting valves and changing header sizes, but it is much better practice to keep the vents open and to allow the water to flow back to the cooling tower under gravity. This is the most flexible and safe way to do it. If your highest exchangers are more than 10m above the towers then you run the risk of vibration in the return piping if you do not keep the vents open.
Keeping the vents open also solves the problem discussed in post #5. If the vents are open and the return is by gravity then there is no effect on the back pressure of the pumps. There will be no interaction between the pumps if the vents set the return pressure to atmospheric. This is the universal way to do it and whoever designed your original circuit knew what they were doing. Leave it that way. Just check that the return piping is big enough for the combined flow under gravity, and that the vertical sections are self venting. Keep it simple.
Thanks to all for your valuable input.
However, still a small doubt in my mind.
Let's assume that
1) all lines are adequately sized, fullfilling requirement of self venting.
2) CT. height is 10 m
In that case the back pressure at common header would be about (1 kg/cm2a (atm press) + 1 kg/cm2a (equivalent to 10 m height) + 0.015kg/cm2 (15m total length x 0.001 kg/cm2/m frictional drop) = 2.015 kg/cm2a
Now from LP header, pressure available at return point due to elevation would be 1 kg/cm2a (atm press) + 1.4 kg/cm2a (equivalent to 14 m height) - 0.015kg/cm2 (15m total length x 0.001 kg/cm2/m frictional drop)= 2.385 kg/cm2a
For HP header, pressure available at return point due to elevation would be 1 kg/cm2a (atm press) + 2.7 kg/cm2a (equivalent to 27 m height) - 0.03kg/cm2 (30m total length x 0.001 kg/cm2/m frictional drop) = 3.67 kg/cm2a
If I am right in my understanding, LP header return pressure is almost same / just above the requirement to overcome system pressure drop after exchanger outlet to common header.
However, for HP header the available pressure is much more than this requirement. At some point it shall be killed, so as to have one pressure level at common point (at header) or it will create back pressure in another system.
Correct me, if I am wrong.
I would like to highlight that the flow requirement at highest elevation user with allowable pressure drop in exchanger as back pressure, have been considered as basis, while carrying out pump hydraulics. In short, pump calculation loop doesnot include downstream system of exchanger. However, common header size have been checked for pressure drop, in order to ensure that pressure gradient available is sufficient to overcome pressure drop in return header.
Kindly help.