I am fairly new to relief system design, and was hoping this forum could provide some clarification on the following issue.
When a R.D and R.V are installed in a series configuration (R.D upstream of R.V inlet) is it acceptable, required, or forbid for the burst pressure of the R.D to be lower than the set pressure of the R.V? For example; the R.D has a burst pressure of 150 psig (0% manufacturing tolerance) and the R.V has a set pressure of 145 psig, protecting a vessel with a MAWP of 150 psig.
ASME UG-127 footnote 52 states: "Use of a rupture disk device in combination with a pressure relief valve shall be carefully evaluated to ensure that the media being handled and the valve operational characteristics will result in opening of the valve coincident with the bursting of the rupture disk."
However, API 520 section 4.3.2.2.2 states that:" When a R.D is installed at the inlet of a R.V, the devices are considered to be close coupled, and the specified burst pressure and set pressure should be the same nominal value."
Could one of the more experienced members shed some light on this?
Thank you in advance.