Dear All
I am currently checking the adequacy of existing relief valves along with its Inlet & Outlet line sizing (& it has become one of my favourite subjects now).
For steam we normally have discharge line open to atmosphere. And invariably many of the times the flow at the end of discharge pipe is Sonic.
In normal cases, since we know the discharge pressure as atmospheric, we estimate the pressure at the outlet of PSV by calculating the pressure drop through pipe & fittings.
In one of the calculations, I got the velocity at the discharge pipe above 1 Mach. I adjusted the inlet & out let pressure so that the velocity is in the Sonic range. But the outlet pressure goes above atmospheric. I discussed in the department & I was told to change the lin size (Agreed)
But the question is, now since the system is already in place, how is the relief valve going to act in case the pressure rises. What would be the discharge pressures & what would be the back pressure at the outlet of PSV. Is it right to assume the line frictional pressure drop as backpressure???
(maybe the excess energy goes as sound that we hear when PSV pops up)
|
Discharge Piping
Started by Guest_Kiran G Parihar_*, Feb 15 2006 06:17 AM
No replies to this topic
Share this topic:
#1 Guest_Kiran G Parihar_*
Posted 15 February 2006 - 06:17 AM
Similar Topics
Piping Design_ Pump PipelineStarted by Guest_anh.phungthai@boydensvn_* , 29 Feb 2024 |
|
|
||
Blocked Outlet For Vessel With Multiple DischargeStarted by Guest_Ghasem.Bashiri_* , 24 Dec 2023 |
|
|
||
Guidance Needed For Sizing A Knockout Drum With Multiple Psv DischargeStarted by Guest_fmalik_* , 04 Dec 2023 |
|
|
||
Answered
Coefficient Of Discharge For Restriction OrificeStarted by Guest_Estiqaatsi_* , 04 May 2023 |
|
|
||
Pump Discharge PresssureStarted by Guest_krishnamurthy_* , 08 Apr 2023 |
|
|