Dear all,
I have some basic doubts arising due to a recent event. I have attached a sketch of closed loop cooling water circuit for our compressors in the excel file. The only parameters which can be monitored are pressure and temperature downstream of the cooler.
Only one of the two cooling water pumps is i/c at any time. Normally, cooling water is sent to only one of the compressors, whichever is in operation. Valve in the make-up line is kept very slightly open so as to allow a little overflow from the overflow line. There is no controller in the discharge line of the pumps.
Here are my doubts,
a ) If water is sent to both compressors simultaneously (without changing make-up flow), we observe a fall in the disch. Pressure. (Generally from 3.5 kg/cm2g to 2.5 kg/cm2g). Does this necessarily mean that the flow rate through the pump has increased putting extra load on the pump? Or does this simply mean that NPSHA has reduced and level of water in the tank has fallen? Or is it a bit of both?
b ) In above case, to maintain the disch. Pressure at 3.5 Kg/cm2g, we now increase the make-up flow slightly. Will the flow rate increase now? Will it put any extra load on the motor?
c ) Finally, will the maximum NPSHA be (maximum upstream make-up pressure + height of the tank)? (if make-up valve is completely open)
What I basically am confused about is:
1) Effect of sending water to both compressors, (without increasing make-up flow) on flow and head of the pump.
2) Effect of increasing the make-up flow(and hence overflow) on NPSHA, flow and head of the pump.
What actually happened follows. Compressor-1 and cooling water pump -1 were running. Compressor-2 had to be started for a routine change-over. Cooling water valve to compressor-2 was hence opened without changing make-up flow. This caused cooling water pump disc. Pressure (P) to fall from 3.5 to 2.5 kg/cm2g. After a short interval, make-up flow to tank was increased until disc. Pressure (P) rose back to 3.5 Kg/cm2g.
Due to certain complications, change-over which normally is over in 30 minutes, could not be completed for the next 3 hrs. During this whole time, cooling water was going to both compressors. After three hours, cooling water pump -1 tripped due to overload and cwp-2 started automatically. 45 minutes later, cwp-2 also tripped due to overload. The reason behind this overload is what I want to understand.
Other problems in the cooling water circuit have not been ruled out though. (higher than expected pressure drop, underperforming motor and such).
Any help is highly appreciated.
Thankfully
Bikrom